It's totally normal.
No it isn't. Under normal circumstances nothing should come out of the vent pipe. Normal expansion is accomodated by the F&E pipe. But this is too slow to mix in chemicals.
Venting aerates the water and accelerates corrosion.
It's totally normal.
Unfortunately bouncing back and forward on a forum where, quite frankly, you are now receiving conflicting and incorrect advice is not helping you sort this out.
or anywhere else where the water can go.
There's no proof of the over pump. Proof is easily achieved with a picture of vented water falling into tank.
The physics would not allow an over pump given the huge column of water inside the vent pipe. I would expect some intermittent overflows when valves shut off. I would expect some dribbles.
Sorry, you lost me there. The F&E cistern water level determines where the water in the vent pipe is ie at the same level as water finds its own level. Air column is NOT infinite or massive or large- it is from water level to open end of vent pipe
Any competent heating engineer know that suction side of pump will be at negative pressure on pumped dude at positive pressure. If you look closely, you would appreciate F&E is configured as close coupled, So, both feed and vent pipes will be at negative pressure UNLESS there is a blockage in the 150mm or less section which makes the vent at higher pressure resulting in pumping over through the vent and sucking down on the body of water in the cistern. Bear in mind the pump is at lowest speed
It has to be further emphasised pump speed is set to overcome system resistance and achieve correct temperature differential and NO pump should be taking place
Of course I could be talking garbage do will be open to education on why the OP is having issues.
OP has said pump is correctly oriented
the 3 way valve suddenly stop feeding into the tank loop.
Either through the ABV or rises up the feed into the cistern.have a guess where the water momentum goes when the pump stops
the pump in an open vent is not there to act as a pump per se, providing any real pressure (head) as such, it is there as a circulator and should only provide enough 'pressure' to overcome the system resistance and excess pressure would then need to find an outlet and the only place there could be would be the open vent and were back to pumping over.It has to be further emphasised pump speed is set to overcome system resistance and achieve correct temperature differential and NO pump should be taking place
you have a 3-port valve that you think can shut both sides at the same time?
that's interesting.
If one flow out of two shuts, the doubled momentum has to go somewhere. So up the vent it goes.
Also it's under a greater pressure from a tank full of water
Regardless of what you think, yes it doesIt doesn't.
Regardless of what you think no it isn't, the water level in the vent may rise by the same amount in the feed as their pressure is the same but it is not designed to vent water over the top unless it's under fault conditionsthe water momentum is dissipated into the vent
No, same pressure in both the feed and vent pipe. It doesn't matter how big the cistern is, it is the height of the water which creates pressure and will be the same for vent and feed.
Having a valve on the vent pipe would allow control of how much venting is done. In this case, it isn't necessary. You incorrectly assume a valve would be there to close the vent off
Open vent CH system design 101, hence why it's called open ventthere should never be a valve on the vent pipe
If they are close together, yes (hence the 150mm rule of thumb).
If they are far apart, they are the same as the DP in that particular part of the system.