Hi all. I’m moving into a new Bellway house. Can a car charger be connected directly to the meter on the outside wall or would it have to be connected to the CU located in the middle of the house? There are many conflicting opinions.
No.Do the regs state that’s it needs to be connected back to the CU?
Not in those words, however circuits must be connected to appropriate protective devices such as MCBs, RCDs, RCBOs or whatever - and installing such things outside is only permitted if those devices are suitably rated for such an environment.Do the regs state that’s it needs to be connected back to the CU?
Unlikely, there are many routes for cables, most of which do not involve them being visible on the surface of a wall.getting the cable outside would be messy and the cable would be visible in the living room or hallway
Some sling it and wing it types like to fit a grotty little consumer unit on the outside wall and call it done. They are wrong.
Some manufacturers may claim that the enclosure is suitable for use outside.There are suitable CUs for outside use
I have worked on sites with WMDU (weatherproof main distribution units) many times, and they are a real pain, to work on them in inclement weather you need to erect a tent first. And in essence they are a DB inside a large metal box, so the weather has two enclosures to get through, and they normally have a small heater inside them. Although the current drawn often made them warm anyway.There are suitable CUs for outside use
Are you saying manufacturers lie?Some manufacturers may claim that the enclosure is suitable for use outside.
The devices inside it most certainly are not suitable for such a location as they will be pollution degree 2.