Hello,
I spent some time reading threads on forums to figure out how my heating system should be wired. I need guidance from those more knowledgable than I.
My current set up consist Intergas Xtreme 36 boiler with two Opentherm inputs. Nest 3rd gen connected to one Opentherm input to control the boiler. Second Nest thermostat E is waiting to be wired in.
I also have 2x 2 port Honeywell V4043H1056 zone valves installed for zone 1 (downstairs) and zone 2 (upstairs).
My intension is to create 2 zone central heating system across the house (downstairs and upstairs as zone 1 & 2 respectively) by using 2 motorised valves and two Nest thermostats (Nest 3rd gen for zone 1 & Nest thermostat E for zone 2) connected to both Opentherm inputs on the boilers PCB.
Would wiring look similar to this diagram created by @stem for similar installation? I'll insert picture of Stem's design into this thread for reference.
I would imagine that Nests connected via Opentherm to the boiler would call for heat and trigger the boiler to fire up instead of motorised valves or it should be wired in the same way as per diagram (valves call for heat) and Opentherm thermostats only control heat demand? T1/T2 on Heat Link would not be used, OT1/OT2 would be used instead and connected directly to the boiler Opentherm inputs (terminal 1/2 X13 & 1/2 X12).
I would greatly appreciate some help on how to get it wired properly.
I spent some time reading threads on forums to figure out how my heating system should be wired. I need guidance from those more knowledgable than I.
My current set up consist Intergas Xtreme 36 boiler with two Opentherm inputs. Nest 3rd gen connected to one Opentherm input to control the boiler. Second Nest thermostat E is waiting to be wired in.
I also have 2x 2 port Honeywell V4043H1056 zone valves installed for zone 1 (downstairs) and zone 2 (upstairs).
My intension is to create 2 zone central heating system across the house (downstairs and upstairs as zone 1 & 2 respectively) by using 2 motorised valves and two Nest thermostats (Nest 3rd gen for zone 1 & Nest thermostat E for zone 2) connected to both Opentherm inputs on the boilers PCB.
Would wiring look similar to this diagram created by @stem for similar installation? I'll insert picture of Stem's design into this thread for reference.
How to connect two new Nest 3rd gen heatlinks? (photos)
should a link from the brown permanent live at terminal 3 to the two grey wires at terminals 4 and 5? Eh?? you said you were using wiring terminals 4 and 5 for the 2 x Heat links 'heating call for heat' Don't see any grey wires at terminals 4 & 5, they appear to be the brown wires to the...
www.diynot.com
I would imagine that Nests connected via Opentherm to the boiler would call for heat and trigger the boiler to fire up instead of motorised valves or it should be wired in the same way as per diagram (valves call for heat) and Opentherm thermostats only control heat demand? T1/T2 on Heat Link would not be used, OT1/OT2 would be used instead and connected directly to the boiler Opentherm inputs (terminal 1/2 X13 & 1/2 X12).
I would greatly appreciate some help on how to get it wired properly.