Its kinda basic (sorry to sound rude)... but if the load exceeds the wire capacity it will trip...
no it won't
(not sorry to sound rude)
Its kinda basic (sorry to sound rude)... but if the load exceeds the wire capacity it will trip...
Yes, they were/are not - 30/0.725 = 41.38A.Do I take it that, for the same reason, 4mm² sockets radials protected by a 30A 3036 were also not possible?
BS 3036 .... 0.725 correction factor....Do I take it that, for the same reason, 4mm² sockets radials protected by a 30A 3036 were also not possible?
its complex as it involves all the above, x3 outside lighting, outside garage RCD and wifi underfloor heating and a X4 multi zone RGBW LED switch in additional to another 3/ 4 lighting zones ALL with a concrete sub floor!
Well, in general it might....Its kinda basic (sorry to sound rude)... but if the load exceeds the wire capacity it will trip...
no it won't
It's a self-build - surely he'll have put suitable ducting in?Something of an embuggerance when it comes to running the cables, if you have a solid floor.
No, I don't think there is any doubt - the arithmetic is clear enough. However, this was a sort-of pre-amble to my follow-up question ...Yes, they were/are not - 30/0.725 = 41.38A. Is there a doubt? Am I missing something?Do I take it that, for the same reason, 4mm² sockets radials protected by a 30A 3036 were also not possible?
I've always thought that the 20A CCC is the minimum figure arrived at for the cable after applying all of the relevant derating factors, which meant not just installation method but includes ambient temperature, grouping, semi-enclosed rewirable factor etc.... are you not at least a little surprised (if not amazed) that 433.1.103 not only allows a ring final cable with a CCC of 20A to be protected by a 32A MCB, but it also allows that same cable with a CCC of 20A to be protected in the same circuit by a 30A 3036 fuse? If such a high degree of 'under-protection from a 3036' is tolerated in a ring final, why is a much lesser degree of 'under-protection by a 3036' not also 'tolerated' in a 4mm² radial?
No.... are you not at least a little surprised (if not amazed) that 433.1.103 not only allows a ring final cable with a CCC of 20A to be protected by a 32A MCB, but it also allows that same cable with a CCC of 20A to be protected in the same circuit by a 30A 3036 fuse?
Because the figures do not match.If such a high degree of 'under-protection from a 3036' is tolerated in a ring final, why is a much lesser degree of 'under-protection by a 3036' not also 'tolerated' in a 4mm² radial?
I see. I've always thought the same, in that 20A CCC is the minium after applying 'all de-rating factors' applying to the cable, but I've never regarded the "semi-enclosed rewirable factor" as being a 'cable de-rating factor'. If you look at 433.1.101, which talks about this 0.725 factor, it talks in terms of In not exceeding 0.725 times the (presumably after application of de-rating factors) CCC of the cable. If they thought the way you are suggesting they would presumably, at most, have reminded one that the de-rating factors applied to the cable's CCC had to include 'the BS 3036 factor' when appropriate.I've always thought that the 20A CCC is the minimum figure arrived at for the cable after applying all of the relevant derating factors, which meant not just installation method but includes ambient temperature, grouping, semi-enclosed rewirable factor etc.... are you not at least a little surprised (if not amazed) that 433.1.103 not only allows a ring final cable with a CCC of 20A to be protected by a 32A MCB, but it also allows that same cable with a CCC of 20A to be protected in the same circuit by a 30A 3036 fuse? If such a high degree of 'under-protection from a 3036' is tolerated in a ring final, why is a much lesser degree of 'under-protection by a 3036' not also 'tolerated' in a 4mm² radial?
See what I've just written to BAS. That is very different from what I have always thought/'understood'. My understanding has always been that the 20A CCC minimum was nothing to do with 3036's but, rather, to facilitate use of 2.5mm² Method A in ring finals - and that, indeed, they had to 'tweak' Table 4D5 to make even that possible.No. 20/0.725 = 27.6A (or 27x0.725 = 19.5A) - near enough. Isn't that WHY 20A minimum is the value required? A tweak.... are you not at least a little surprised (if not amazed) that 433.1.103 not only allows a ring final cable with a CCC of 20A to be protected by a 32A MCB, but it also allows that same cable with a CCC of 20A to be protected in the same circuit by a 30A 3036 fuse?
Well. you can't get away from the 0.725 factor with 3036 fuses so I do not understand why you would have thought that.See what I've just written to BAS. That is very different from what I have always thought/'understood'. My understanding has always been that the 20A CCC minimum was nothing to do with 3036's but, rather, to facilitate use of 2.5mm² Method A in ring finals - and that, indeed, they had to 'tweak' Table 4D5 to make even that possible.
It is.If what you and BAS have suggested were a correct interpretation, it would mean that 2.5mm² could not be used in a ring final on a 30A 3036 if there were any de-rating factors to b applied to the cable. Is that your belief?
I really don't know what to think! Fortunately 3036's are a dying breed, so it's relatively unimportant, but what you and BAS are suggesting is, as I've said, totally different from what I've always thought and believed.Well. you can't get away from the 0.725 factor with 3036 fuses so I do not understand why you would have thought that.
433.1.202 now.Since 433.1.101 talks about "0.725 times the CCC of the cable", I have always presumed that they were not intending that the "CCC" had already been reduced by a factor of 0.725 if it were protected by a 3036 (otherwise that factor would get applied twice). I have therefore always assumed that 'CCC' took into account installation method and all 'cable de-rating factors', but not any adjustment for a 3036.
No. With 3036s it has to be derated by 0.725That makes total sense to me. The "current-carrying-capacity" of 2.5mm² Method C is obviously always going to be 27A, no matter what the type or rating of OPD.
It has to be able to carry more overload when protected by 3036s.The cable does not suddenly become able to safely carry more, or less, current just because of the type of OPD protecting it.
Isn't that contradicting what you just wrote?The only difference relates to the OPD.
Yes, precisely.With an MCB, the maximum permissible In to protect that cable is 27A, but with a 3036, the maximum permissible In to protect that cable is about 19.6A.
It doesn't matter which way round you do it.However, the cable has a "CCC" (by any sensible definition) of 27A in either case.
If the cable has for other reasons been derated to 20A then it is too small to be used - in a ring - with a 30A 3036.If that interpretation were all correct, then 433.1.103 would be very clear in saying that 2.5mm² cable with a CCC (after application of all de-rating factors other than any adjustment for 3036) of 20A in a ring final is allowed to be protected by a 30A 3036.
I do not understand that, either.I need to think more, but my interpretation seems fairly logical to me. If you say that, for a cable protected by a 3036, "CCC" already includes a 0.725 adjustment for the type of OPD, then, as above, 433.1.101 makes no sense.