You really can't have it both ways. If you want to say that, when protected by a 3036, the "CCC" is 'de-rated' by 0.725, then that means that, in that situation, the "CCC" of Method C 2.5mm² would be about 19.6A. 433.1.101 (or 433.1.202 for those with a BYB) says that the In of the fuse must not exceed 0.725 times the "CCC" of the cable. If, as you above, you believe that the "CCC" is 19.6, then the reg would require that In of the fuse must not exceed 0.725 times 19.6A, namely about 14.2A (27A x 0.725 x 0.725) - which I doubt that even you believe is what is intended433.1.202 now. I'm not sure I understand why you think it is applied twice.Since 433.1.101 talks about "0.725 times the CCC of the cable", I have always presumed that they were not intending that the "CCC" had already been reduced by a factor of 0.725 if it were protected by a 3036 (otherwise that factor would get applied twice). I have therefore always assumed that 'CCC' took into account installation method and all 'cable de-rating factors', but not any adjustment for a 3036.No. With 3036s it has to be derated by 0.725That makes total sense to me. The "current-carrying-capacity" of 2.5mm² Method C is obviously always going to be 27A, no matter what the type or rating of OPD.
That's just, IMO, a very confusing use of the word "overload". The maximum amount of current a cable can safely carry ("CCC") is obviously the same, regardless of the OPD. What differs between an MCB and a 3036 is what multiple of the OP's In that CCC represents.It has to be able to carry more overload when protected by 3036s.The cable does not suddenly become able to safely carry more, or less, current just because of the type of OPD protecting it.
All this is obviously based on the assumption that an MCB may allow 1.45 times its In to flow for up to an hour, and that a BS 3036 fuse may allow 2.0 times its In to flow for up to an hour. The tabulatated values of 'CCC' (Iz) assume an MCB - hence if the tabulated Iz is, say, 20A, that means that the cable is deemed to be able to safely carry 29A (20A x 1.45) for an hour. A 3036 which would allow 29A to flow for no longer than an hour would have an In of 14.5A (29A / 2.0). The 0.725 difference between those two figures (e.g. 14.5A/20A=0.725) arises simply because the 1.45In/2.0In=0.725.
Not at all. As above, a cable with a CCC of say, 20A, has to be able to safely carry 29A for up to an hour, regardless of the nature of the OPD. All that differs (between an MCB and a 3036) is what In of the OPD is necessary in order to limit the duration of that 29A to no more than an hour.Isn't that contradicting what you just wrote?The only difference relates to the OPD.
That's exactly what I've written above, provided your'e talking about the 'fusing factor' to ensure operation within an hour.MCBs have a fusing factor of 1.45 - the standard - 3036s have a fusing factor of 2 so the cable must be derated (2x0.725 = 1.45)
No-one is disagreeing with that, in the 'general' (non-ring) situation. It is the wording of 433.1.101 (or 433.1.204) for ring finals that is the issue.You either have a 27A cable but must protect it with a 19.5A 3036 or you have a 27A 3036 but must use a 37.24A cable.
It does, and that is the point I am "going on about". Iz (aka 'CCC') is a characteristic of a cable given a certain installation method etc. and does not, as far as I can make out, include any adjustment because of the OPD by which it is protected (i.e. the 0.725 for a 3036) - which I presume is why 433.1.101 says that you have to multiply the "CCC" by 0.725 if it's protected by a 3036. If, as you seem to be suggesting, th "CCC" will already have been adjusted by one factor of 0.725 (if protected by a 3036), then applying 433.1.103 would apply a 0.725 factor for a second time - which is obviously not intended. I therefore conclude that "CCC" does not itself include an adjustment for 3036 protection (if that is what is protecting it!).433.1.101 states that the In of the 3036 shall not exceed 0.725 the Iz of the cable.
Kind Regards, John