Hi,
I am hoping some of you can help. I hired an electrician to carry out work on my property. His website stated he was NICEIC registered but I now know he is not. He is apparently NVQ Level 3??? how competent is this person??
I was so scared of the work he had done that I arranged a report to be carried out by another registerd NICEIC company. They found 13 faults and I am now taking my electrician to go to Court for loss of money with having to get another compoany to correct the work (a registered company)
I have put come pics on so you can see what his work was like, what do you think?
Can someone please explain to me what this report is all about as in the dangers if these faults were not found such as electrick shock, can cause fire, remove plaster if problem in future with electrics???? I would like to have a good idea of what I am saying in court when this report is read out so just want to be a bit educated and a bit knowledgeable as I have been very confued with the whole thing, you know if he was not registerd should he have notified the council of the work he was going to do, he worked in every room in my house, lowered sockets, added sockets in kitchen, added new sockets in living room and dining room. The downstairs in my house is concrete floors and he did not feed new cables throough just joined cable with crimps which was then going to be plastered into the walls.
Faluts found by the NICEIC company
1)The "Ring Main" supplying the socket outlets was incorrectly and very dangerouly connected over two fuses (mcb's) one leg on a 30A and second leg on a 40A Mcb
2) We tested out the ring main - socket circuit and found -
* No continuity with Neutrals (break somewhere)
* No continuity with Earths (break somewhere)
3) We later upon further investigation traced this to nails/screws driven into cables R/Hand lounge fire place & R/Hand D-Room fire place
4) Some circuits within fuse board were not protected by RCD's
5) All of the socket outlets down stairs had been lowered from a height 0f 450mm to 200mm - the cables were dropping from above someone instead of rewiring the short cables had extended every one with "crimps" and covered these with capping.... On closer examination most of the crimped connections were loose and just pulled apart - potentially a very dangerous situation
6) thro-out the property "wiring zones" ie permitted area's to coneal cables within walls had been totally ignored - with zig zagging across walls taking the shortest routes
7) Boiler was incorrectly connected to the off peak supply
8) The "earth conductor" was undersized for the type of earthing - TNC's
9) The earthing to pipework had been cut - no bonding to gas and water pipes
10) There was a "LIVE" cable left floating under floor board in bathroom
11) Further testing showed not earth continuity on down stairs lighting circuit
12) In several instances we found switches/sockets hanging off walls - with exposed cable cores
13) The kitchen area wiring can best be described as "a rats nest"
How bad is the work my electrician done for me, is it the work of a cowboy?
Thanks in advance hopefully it's not too long, 7 photo's
View media item 37139 View media item 37138 View media item 37140 View media item 37141View media item 37142View media item 37143 View media item 37144
I am hoping some of you can help. I hired an electrician to carry out work on my property. His website stated he was NICEIC registered but I now know he is not. He is apparently NVQ Level 3??? how competent is this person??
I was so scared of the work he had done that I arranged a report to be carried out by another registerd NICEIC company. They found 13 faults and I am now taking my electrician to go to Court for loss of money with having to get another compoany to correct the work (a registered company)
I have put come pics on so you can see what his work was like, what do you think?
Can someone please explain to me what this report is all about as in the dangers if these faults were not found such as electrick shock, can cause fire, remove plaster if problem in future with electrics???? I would like to have a good idea of what I am saying in court when this report is read out so just want to be a bit educated and a bit knowledgeable as I have been very confued with the whole thing, you know if he was not registerd should he have notified the council of the work he was going to do, he worked in every room in my house, lowered sockets, added sockets in kitchen, added new sockets in living room and dining room. The downstairs in my house is concrete floors and he did not feed new cables throough just joined cable with crimps which was then going to be plastered into the walls.
Faluts found by the NICEIC company
1)The "Ring Main" supplying the socket outlets was incorrectly and very dangerouly connected over two fuses (mcb's) one leg on a 30A and second leg on a 40A Mcb
2) We tested out the ring main - socket circuit and found -
* No continuity with Neutrals (break somewhere)
* No continuity with Earths (break somewhere)
3) We later upon further investigation traced this to nails/screws driven into cables R/Hand lounge fire place & R/Hand D-Room fire place
4) Some circuits within fuse board were not protected by RCD's
5) All of the socket outlets down stairs had been lowered from a height 0f 450mm to 200mm - the cables were dropping from above someone instead of rewiring the short cables had extended every one with "crimps" and covered these with capping.... On closer examination most of the crimped connections were loose and just pulled apart - potentially a very dangerous situation
6) thro-out the property "wiring zones" ie permitted area's to coneal cables within walls had been totally ignored - with zig zagging across walls taking the shortest routes
7) Boiler was incorrectly connected to the off peak supply
8) The "earth conductor" was undersized for the type of earthing - TNC's
9) The earthing to pipework had been cut - no bonding to gas and water pipes
10) There was a "LIVE" cable left floating under floor board in bathroom
11) Further testing showed not earth continuity on down stairs lighting circuit
12) In several instances we found switches/sockets hanging off walls - with exposed cable cores
13) The kitchen area wiring can best be described as "a rats nest"
How bad is the work my electrician done for me, is it the work of a cowboy?
Thanks in advance hopefully it's not too long, 7 photo's
View media item 37139 View media item 37138 View media item 37140 View media item 37141View media item 37142View media item 37143 View media item 37144