Yes but 433.1.204 begins with, within commas, "with or without unfused spurs" and nowhere does it mention that it applies to the spurs. If it did apply, do you contend that a 4mm² spur with two double sockets would require 13A protection or the 4mm² is not allowed even though its CCC is >20A.
It's not the spur itself that is the issue,
...but that's what we're talking about.
but what it is fed from. An unlimited number of sockets is obviously acceptable if all wired in 4mm² cable all the way back to a 32A MCB in the CU (i.e. a standard 32A radial). However, what would you say about the acceptability of that circuit if I told you that the last 2 metres of cable back to the CU was to be in 2.5mm² cable, in parallel with 48 metres of 2.5mm² cable (i.e. such that 96% of the total current went through the 2m length of 2.5mm cable). Would you still regard that circuit as acceptable?
No, of course not but I keep saying that is for the designer to consider.
Indeed - but that's the whole discussion we've been having recently. The reality is that, without a crystal ball, a designer cannot know how a sockets circuit is going to be loaded - but the general view seemed to be that, given that truth, a designer is allowed to work on the basis of what (s)he believes is "likely".
All socket circuits must, by nature, be like that.
As discussed, were that not the case, it would not ever be possible to design a sockets circuit which had multiple sockets, particularly not a 20A radial,
You cannot design a socket circuit , other than avoid what may be obvious as wrong - high demand spur(s) near one end (as you say) , a huge kitchen where the demand is bound to be too high.
Apart from single 20A demand circuits (which may be added to by the unknowing) I can think of no reason to install a 20A radial.
People talk as if 2.5mm² is all there is available.
Splitting into two 20A radials is often quoted as a solution, albeit temporarily permanent, for a fault in a ring circuit so it is fundamentally flawed, then.
since there could be no certainty that the load would never exceed the In of the OPD.
Again, that is the nature of socket circuits.
I would say that example is alright because there is still 16A protection and even if someone changes it to 13A that is still 26A and alright.
Maybe, but that doesn't alter the fact that we see people being told that it is 'not allowed' If you feel that "26A is still alright" (presumably assuming Method C installation) would you feel that (despite Appendix 15), it would be 'alright' to have an unfused spur supplying two single sockets?
Yes, electrically, it obviously is - leaving aside the fact that 'no one' 'knows' you're not supposed to put two 13A loads in a double socket.
We see people being told all sorts of things.
I cannot believe Appendix 15 did not show two singles because people are supposed to know about the double socket 'limit' and therefore would know it is wrong.
Perhaps they did not show it because it is obviously alright and everyone should know
that.
More likely, it is not shown because it is not possible to show everything.
It does not show two single sockets in 15B; what does that mean - not allowed?
Why is Appendix 15 there at all?
433.1.204 makes no mention of it.