OK, so are you now revising your previous statement to say that you only consider a 4mm² unfused spur (from a 2.5mm² ring final) supplying multiple sockets is only OK if it originates more than X% of the ring length from one end of the ring? ... and, if so, what is your value of 'X'?
I don't think I said that.
Maybe not in exactly those words - but you started by telling the OP that using 4mm² cable "would suffice" for feeding an unlimited number of sockets as an unfused spur from a ring final (without qualification, and without knowing where that spur originated), but when I presented you with an explicit example, you effectively said that it would
not be acceptable if the spur originated at only 4% of the way around the ring. You therefore presumably must have some 'threshold' in mind.
I haven't worked out the value but you have several times but probably more than the 2m in your above example.
Well, I've worked out the '
worst/best case scenario', both for 20A and 27A CCC, (i.e. the distance from the end of a ring beyond which even a 32A load at a single point cannot result in any cable being overloaded) - but I don't know if you would want that degree of certainty. If you did, and if one assumed a CCC of only 20A, then that wouldn't leave you much of the ring to which you could attach a 4mm² unfused multi-socket spur.