Sorry, not worded as clearly as I could have done: I meant call 20A the design current if you like, but it still doesn't stop somebody putting a 26A load at the end of a cable which, according to the regs., need only be rated for that 20A design current but which is protected by a 30 or 32A device."If you like"? It's not a whim of mine - that really is what it stands for.
No, but in other cases the rating of the cable is equal to or higher than the rating of the protective device. Diversity of use with appropriate design of circuit layout means that we hope that the circuit rating will not normally be exceeded by such use, but if it does happen, the cable is protected.If you have a final circuit with 20 sockets on it there is simply no way to guarantee that somebody won't plug 20 13A loads into it at some point.
Neither am I.I'm not a fan of ring finals
As above. I'm not saying that a radial cannot be overloaded, but if it's wired per the regs. the cable is protected adequately and a fuse will blow or an MCB trip before it can become damaged. The exemption for both the ring itself and spurs to have the cable rating equal to or exceeding the fuse rating then goes completely against that basic principle.But can you explain why a 32A ring can be overloaded but a 32A radial cannot?
On the diversity issue, the regs. have always seemed rather inconsistent right from the early days of rings. Why, for example, did they decide that a 30A ring could supply four dozen sockets all around a house (up to 1000 sq. ft.) while a 30A radial was restricted to six sockets?