If a designer is to take account of that when choosing a cable size then he must not use any DSOs in his design, for exactly the same reason.
Presumably you mean any doubles which are not expressly rated for 26A maximum by the manufacturer?If a designer is to take account of that when choosing a cable size then he must not use any DSOs in his design, for exactly the same reason.
That raises issues of the extent to which the designer can impose an ongoing compulsion to use such sockets when any are added or replaced. The point I was making was if you say a designer must eschew the use of a cable with a CCC of 20A to supply a DSO in case someone uses it for 2x13A loads then he should likewise avoid DSOs in the first place.Presumably you mean any doubles which are not expressly rated for 26A maximum by the manufacturer?
Mmm. To what extent should designers be held responsible for misuse of equipment operated outside its specification?That's a very good point: Is it responsible to install a "twin 13A socket outlet" which the manufacturer states is only safe up to 20A total load if it could be called upon to carry a continuous 26A load?
BS 1363 does not require socket outlets to withstand more than 20A in the supply cable.Should such doubles be installed only on 20A radials and not 30/32A radials or rings?
Surely unless we are all labouring under a misapprehension, if BS 1363 does not require them to survive loads of more than 20A, then without any extra claim to the contrary isn't that what every manufacturer who states BS 1363 compliance is saying?Do any manufacturers state that their twin 13A socket-outlets are only safe up to 20A total load?
As I've said before, I think that, strictly speaking, that probably would be the correct course.If a designer is to take account of that when choosing a cable size then he must not use any DSOs in his design, for exactly the same reason.
One would certainly expect them to be shouting their 'better than required by BS1363' performance from hilltops but, if for some reason they chose not to, there is no reason why they can't claim 'compliance with BS1363' even if their product exceeds the requirements of that Standard.Surely unless we are all labouring under a misapprehension, if BS 1363 does not require them to survive loads of more than 20A, then without any extra claim to the contrary isn't that what every manufacturer who states BS 1363 compliance is saying?Do any manufacturers state that their twin 13A socket-outlets are only safe up to 20A total load?
Is the plate screw on that socket screwing into the brown wire that is positioned behind the screw lug? There is also a lot of exposed copper on the line and neutral wires which isn't ideal.I've ony changed one of the sockets so far, wired up exactly as the last one was.
You can either fit all the earth wires from the back box earth terminal to the switches earth terminal. Or run a 1.0mm² earth wire from the back box earth terminal to the earth terminal on the switch.Can I earth the metal plate using one of the earth wires at the back of the box?