Well, I wish I was there when he serviced the boiler, as im still baffled as to why he changed that 13A fuse to a 3A. he even made the point of saying “its amazing how many times I’ve had to change that fuse in other houses”
As an electrical designer, that original 13A fuse makes perfect sense to me. The cable feeding the boiler, from the spur is sufficiently sized to carry 16A, therefore, Ib< In< Iz. Thus the 13A CPD was safe, and coordinated with the 3A PCB CPD, allowing the CPD closest to the potential fault to fail first.
What he’s done is completely shafted the coordination between the upstream and downstream CPDs. So if a fault occurs on that cable feeding the boiler, you really want the fused spur to break first, but in reality either one will go.
please tell me im not going insane!
I usually bypass all that waorkinh out, although more than capable , i find it much quicker to give the MI's a check, generally on boilers it 3amp some are 5