Practical Guide to Inspection I tried the first and second quiz and am glad I have my C&G2391 because the way the questions are worded I found it hard.
I looked at first question on quiz 2 and thought sure answer is "Skilled" but that was not an option. Sure that "Competent" has now gone.
IP2X = 12.5mm and IPXXB is protected against finger I have always considered them to be same. Is there any point asking which one?
2) An Electrical installation certificate requires the due date of the first periodic inspection and test to be recorded by
OK the Designer sets out first test which is normally done as the installation is completed if the tester finds faults he can ask for a test earlier than what the designer asked for so the person carrying out the first test will set the date for second test and the first first periodic inspection and test is in fact the second inspection and test as the first is not the periodic. So there is no fixed answer.
Is 0.2 to 2MΩ to be read as 0.2MΩ to 2MΩ or 0.2Ω to 2MΩ if latter then two correct answers.
"a test on main protective bonding" does not really describe testing the resistance of an earth rod or DNO earth terminal.
Restrictive conductive location means conducting location with restricted movement it seems they are trying to confuse the student.
18 ) A metallic earth return path would be found in a
All but TT but
18 ) A dedicated metallic earth return path would be found in a
TN-S only. Again poor questions.
20. The trip rating of an RCD used for additional protection should be
Well because 300mA and 500mA were not options it had to be 30mA but should it not say if that additional protection is for personal or fire and if on a CONSTRUCTION AND DEMOLITION SITE INSTALLATIONS or elsewhere?
I think the setters need to go and learn English and how to ask questions without ambiguity.
I looked at first question on quiz 2 and thought sure answer is "Skilled" but that was not an option. Sure that "Competent" has now gone.
IP2X = 12.5mm and IPXXB is protected against finger I have always considered them to be same. Is there any point asking which one?
2) An Electrical installation certificate requires the due date of the first periodic inspection and test to be recorded by
OK the Designer sets out first test which is normally done as the installation is completed if the tester finds faults he can ask for a test earlier than what the designer asked for so the person carrying out the first test will set the date for second test and the first first periodic inspection and test is in fact the second inspection and test as the first is not the periodic. So there is no fixed answer.
Is 0.2 to 2MΩ to be read as 0.2MΩ to 2MΩ or 0.2Ω to 2MΩ if latter then two correct answers.
"a test on main protective bonding" does not really describe testing the resistance of an earth rod or DNO earth terminal.
Restrictive conductive location means conducting location with restricted movement it seems they are trying to confuse the student.
18 ) A metallic earth return path would be found in a
All but TT but
18 ) A dedicated metallic earth return path would be found in a
TN-S only. Again poor questions.
20. The trip rating of an RCD used for additional protection should be
Well because 300mA and 500mA were not options it had to be 30mA but should it not say if that additional protection is for personal or fire and if on a CONSTRUCTION AND DEMOLITION SITE INSTALLATIONS or elsewhere?
I think the setters need to go and learn English and how to ask questions without ambiguity.