A way to check without spending any money on secondary meters etc would be to switch every single breaker off on your consumer unit for 24 hours which should be ok if the house isn't always in use.
Obviously, it should be the same reading at the start and end of this period.
Next test, Switch on only one ring main and unplug every appliance from the ring. Plug in one 100W light bulb and leave it on for 10 hours. Your meter should have moved by 1kWh only.
If in the 1st test the meter moves then it may not be trimmed properly so is moving its self, or there is a sneaky circuit taking load.
If its not moved then there is no problems there.
In the 2nd test, if the reading is 1kWh then i would think there is no problems. If its more than this, then its probably running fast.
If it has logged, say, 2.5kWh, then we know its running 2.5x faster than it should.
The 100W lightbulb test will be give or take 10%, so your reading will be 1.1 or 0.9kWh because the bulb may not be using exactly 100w.
I agree with other posters tho, the only sure way is to buy a new meter like
http://www.tlc-direct.co.uk/Products/RDCRED100.html for £25 and get a friendly electrician to fit it.
Take a photo, ideally showing the two meter readings side by side then come back a week later.
You said
They have used 2000 pounds worth of electric ontop of there normal bill
then
bill that is now almost 4000 pounds for a quarter
Your implying £2000 a quarter of normal usage which is huge! I'm all electric heating and use that year for both domestic and heating consumption.
At 15p/unit (npower average rate info i just found), £2000/q is 4430 units per month meaning an average demand of 146kWh per day.
I would estimate this to be in the order of 10-20 times what i'd expect from the laods and usage you indicate. Your then saying that the meter is logging £4000/q, or 8860 units per month, or 292kWh per day. Is as if you have a 12kW electric shower running 24x7!!!
Im assuming you don't have electric heating? (storage, panel, electric boiler etc)
As for sneaky loads, to use that amount of electricity implies a huge sneaky load.
The sort of thing that you sometimes see are a 3kW fan heater in a loft, garage, greenhouse etc there for frost prevention but the thermostat has it running all the time.
If there are 500w or 1000w halogen floodlights on; hundreds of meters of trace heating on pipes, etc etc. are other culprits.
Even with that, i cant see where the "normal bill" of £2000/q is, never mind the £4000/q is coming from!
Stuart