Is this perhaps a recognised phenomenon? I initially thought that it was just a fluke (of my Fluke!), but it is so consistent that I now find that hard to believe.
Whenever I measure (estimate) the Re of one of my earth rods by measuring the loop impedance of the rod (in isolation), the first measurement I get is always appreciably higher (usually to the tune of ~50Ω than all subsequent measurents over the next few hours.
For example, this morning (with my Fluke 1652) I got an initial result of about 120Ω. An immediate repeat (within seconds) gave a result of about 70Ω and several repeats over the following 3-4 hours gave similar results, not varying from the second reading (i.e. ~70Ω by more than an ohm or three.
As I asked, is this a 'known phenomenon' and, if so, what is the explanation? Is it perhaps some sort of electrolytic phenomenon - although the test waveform is described as 'sinusoidal', it's duration is only 10mS (i.e. one half-cycle at 50Hz {assuming it does use 50Hz!}) - so, if it starts at zero crossing, it will actully be effectively DC.
... or is there some other possible explanation? Given the consistency of measurements (excluding the initial one), I find it hard to believe that the meter is faulty - but I suppose anything is possible.
Kind Regards, John
Whenever I measure (estimate) the Re of one of my earth rods by measuring the loop impedance of the rod (in isolation), the first measurement I get is always appreciably higher (usually to the tune of ~50Ω than all subsequent measurents over the next few hours.
For example, this morning (with my Fluke 1652) I got an initial result of about 120Ω. An immediate repeat (within seconds) gave a result of about 70Ω and several repeats over the following 3-4 hours gave similar results, not varying from the second reading (i.e. ~70Ω by more than an ohm or three.
As I asked, is this a 'known phenomenon' and, if so, what is the explanation? Is it perhaps some sort of electrolytic phenomenon - although the test waveform is described as 'sinusoidal', it's duration is only 10mS (i.e. one half-cycle at 50Hz {assuming it does use 50Hz!}) - so, if it starts at zero crossing, it will actully be effectively DC.
... or is there some other possible explanation? Given the consistency of measurements (excluding the initial one), I find it hard to believe that the meter is faulty - but I suppose anything is possible.
Kind Regards, John