Where is the board for the loft, have you run cables back down the house for the circuits you mentioned?
Ir tests tend to be done on existing circuits and new circuits when built and ready for service.
The logic being that say a ring could be 35m end to end, with x number of sockets between those ends and at each of those sockets a termination might not be screwed down correctly, it may of simply become loose, the cable may be old, poorly stripped back, eaten (by vermin), soaked etc, etc.
On complete circuits you would expect the ir to be low, the higher it is the more suspect it could be.
Dump the ir test until built and just test the function via...
Use choc blocks is you want and then do end to end continuity of the ring, and on the radials close down a pair at a time on the far end (LN, LE, NE),
Since your not testing for certificated results, even a simple buzzer would do.