It must be time for frost stat questions

Joined
24 Nov 2013
Messages
391
Reaction score
18
Location
Berkshire
Country
United Kingdom
So my heat only boiler has two low-voltage terminals for the frost stat. If left open the boiler will turn on so if there is no frost stat present a link needs to be put in to join the terminals. But I want to put in a frost stat .....

I've been scratching my head wondering how am I going to connect up a regular Drayton frost and pipe stat. I think I've figured it out but is this the normal way of doing it ? It seems complicated even though I have managed to do it without extra relays etc.

Please see attached I hope its self-explanatory. It should say "Boiler Connections" and I've only shown the 2 relevant ones. For the boiler to turn on, I think both stats need to be calling for heat which is the same for regular S-Plan systems I think...

Note that my existing Drayton Frost Stat doesn't give access to the "satisfied" terminal so I plan to buy another which does. The pipestat does give access to all 3 terminals (Common, Satisfied, Call) so I think I can reuse that.
 

Attachments

  • IMG20241121220229.jpg
    IMG20241121220229.jpg
    190.7 KB · Views: 21
Sponsored Links
The frost stat and pipe stat are wired in series, both have to 'call for heat' [i.e. be on] for the boiler to operate. Starting from a cold heating system, they work like this:

1. The temperature where the frost stat is located falls below the setpoint, so 'calls for heat'. [on] Because the heating system is cold the pipe stat is also 'calling for heat'. [on]

2. The heating system starts up and hot water circulates through the heating system.

3. The water in the pipe where the pipe stat is located reaches the set point and switches the heating off

4. After a time the pipe where the pipe stat is located cools and switches the heating back on. Steps 3 and 4 repeat until:

5. The area where the frost stat is located is above its set point and switches the heating off.

456.jpg
 
Last edited:
I must admit is seems odd, the whole idea of a frost stat is to run when otherwise the heating would not run, so I would have expected to find a parallel connections, but I note many boilers have a separate connection for the frost stat, never really considered why.

Maybe just for ease of connecting. So I have looked at a random set of instructions
2-stage frost-protection system – the frost-protection system protects the appliance against the risk of frost damage. The first stage enables activation of the pump should the temperature of the appliance fall to 7°C. The second stage becomes active when the temperature has dropped to 3°C. Should the second stage become active, the appliance will function on minimum power until it reaches 30°C.
seems I was wrong, however after reading this, I would say reading the installation manual for your boiler is the way forward, the system used very likely changes boiler to boiler, one can't assume, you must actually read the instructions.
 
Sponsored Links
so I would have expected to find a parallel connections
So would I. I don't think the description you posted covers it either, it only protects the boiler, not other parts of the CH system, or water supply pipework and tanks. It also needs a froststat (subject to air temperature), in the coldest part of the house.
 