davy_owen_88 said:Most loads assumed to be purely resistive such as showers give their ratings for both 240v and 230v. The highest rating obviously belonging to the 240v rating.
9.5kW @ 240v = 39.58A
9.5kW @ 230v = 41.30A
When the real rating at 230v is = 8.7kW so 37.82A
Nothing wrong with installing higher rated cables and higher rated MCB's but for this guys case, 40A should do.
Adam_151 said:The 'headline' rating on shower boxes is generally at 240v, at least on the ones I've seen, it says something like "9.5kw@240v, 8.7kw@230v" I suppose strictly speaking you should use the 230 rating and calc using 230 (as you would do if you only had a 230v rating), but that just seems a tad daft when the voltage is 240v in the real world, using the headline (240v) rating and using 230 in your calculation won't do any harm though, just gives you a design current figure a tad bigger than the real world one and leaving breakers with some 'headroom' is good practice because they can run cooler, etc (I believe the NEC across the pond calls for the design current to be no more than 80% of the nominal current of the breaker for reasons upon this line of thought)
EDIT: So after all that, I'd say use the rating @240v and use 240 when you find the design current
C&GStudent said:I use 230 all the time.
As the voltage is closer to 240 you know the current will always be a little bit less than you calculated. Which is nice!
bernardgreen said:C&GStudent said:I use 230 all the time.
As the voltage is closer to 240 you know the current will always be a little bit less than you calculated. Which is nice!
WRONG
The only constant is the resistance ( other then a slight variation with temperature )
Therefore if more volts then more amps and more watts.
If an item is rated as 2 Kwatts at 230 volts and is a resistive load
then the resistance is 26.45 ohms
W = V² / R which is (230 * 230) / 2000 = 26.45 ))
So the resistance is 26.45 ohms
Current when 230 volts is applied will be 230 / 26.45 = 8.69 amps
Current when 240 volts is applied will be 240 / 26.45 = 9.07 amps
EddieCurrent said:Hello,
On a recent course I was informed that 230 is to be used when doing all calc's , except PFC , why I dont know .....
Ill informed ???
ricicle said:It is an interesting subject this because if you look in the regs for max Zs for MCBs the table header says it is based on a Uo of 230V but if you look at the figures they are based on 240V (type B 5X, type C 10X, type D 20X)
If the Uo was in reality lower than 240V then less fault current would flow for a given Zs and perhaps the MCB would not trip instantaneously (still maybe quicker than 0.4 sec)
newspark_paul said:Third, why complicate things further by looking at resistive loads to drop the current further? The original post dealt with a breaker for a domestic shower, not a complicated industrial install.