It's nothing new. We started thinking, and exposing the apparent flaws in the regs as regards supplementary bonding, a good few years ago.Glad I’ve got you all thinking - it’s not as cut and dried as the initial responses is it …
One of the reasons it's not discussed a lot more these days is that it has become almost moot, because there are few real-world situations in which the regs will still require SB, even in bathrooms - so the issue is no longer of much other than academic interest.
In the example I gave, if the R1+R2 of the circuit with a fault was about 0.16Ω - but you need to realise that I just pulled numbers out of the air, 'as I was typing', to illustrate the point I was making. The conclusions would be essentially gthe same even if I had used more frealistic figures.Hmm but How/in what scenario could the fault current achieve 500 A ?