Lectrician, Thanks for the advice...
Lectrician said:
If you are running new cables - why not just run a 4mm radial for the couple sockets (or even 2.5) on a 32 or 20amp respectivly.
I want to limit the number of cables I run because of the difficulty of the route (see below). If the 4mm² cable isn't really enough for the Aircon and the sockets together, I'll scrap the sockets idea - it was just a convenience thing "while I was there".
Lectrician said:
For the aircon, no RCD required. Fit 20amp IP56 isolator adjacent external compressor, and wire to this in 4mm on a 20amp breaker (C type), again, depending on run, 2.5 may be ok but would need calculating.
I'm not sure this is necessary - because of the "DC Invertor" aspect of this unit, it's powered from the indoor unit, and I'd much rather isolate the whole thing than just half of it - and there are four conductors (plus Earth) connecting the two units, so I'm not even sure if there is mains between them, let alone which ones to switch/protect! The instructions make no mention of any switching or breaker between the units, just the on the feed to the indoor one.
Lectrician said:
What is this conduit you talk of - 15mm internal diameter?? And where is it run??
This house was built in 1937 and wherever cable runs are buried in walls they are in thin-walled steel conduit, either about 10mm or 15mm interrnal diameter - probably actually 3/8" and 5/8", considering its age. The mains comes in under the stairs, and since the top three steps are winders, there is no way to go directly upwards from the understairs cupboard to the underfloor upstairs. So when they built the house they installed six of the larger sized conduits between the ceiling of the cupboard, upwards and through the wall that seperates the bathroom from the top of the stairs, into the underfloor in the bathroom. They're about two feet long and they are the only way to run cables from the CU to upstairs. When the house was built there were only four circuits (lights, immersion heater, up and down rings) so I'm rather glad they saw fit to put in six conduits! But I now have only one left unused, so one 4mm² cable is pretty much the limit for this project.
Lectrician said:
Air con pipes that travel from inside to out need main eq bonding - most units come with a stud ready for this on the internal or external unit - rarely used - but should be!
That's something I hadn't thought of, and isn't mentioned in the instructions. Isn't the fact that they are connected to the units themselves at each end, and these are earth bonded, be good enough? When you say there is a stud (I haven't looked yet), does this mean you bond the pipes to it, or bond it to the house Earth? And where do you get Earth clamps for 1/4" and 3/8" pipes?
Cheers,
Howard