holmslaw
..
Exactly, so if there is a potential risk of it coming into contact with water, it would seem wise to have something in place that will disconnect the supply should that situation arise.It's unwise to have any mains power in contact with water.I would personally have thought it wise to have RCD protection for an item of electrical equipment that could possibly fill up with rain water.
ReallyHow large is tne motor in this unit ?
Any motors larger than 1 Kw are considered as "disturbing loads" by the Distribution Network Operator and I believe have to be notified to the DNO.
The application for a new supply I have just completed required notification of motors greater than 1 Kw as well as any welding equipment that might be used on the supply.
When you or whoever originally applied for a connection to the DNO's distribution system, you declared what load you would want. The connection would then be provided to cater for that load. If you want to add additional load, you should ask to redeclare your load requirement. If you're unlucky some jobsworth will get hold of your request and charge you an arm and a leg to modify your connection.There must be an awful lot of DIYers with loads such as that that have never notified anything, is it a new requirement ? I guess I'd better keep quiet about the 3hp pressure washer, 3hp compressor (nearly had a 4hp but not enough room for it), various other machines, stick welder, MIG welder .. and my mates MIG welder that really could do with a 32A supply (we just keep it turned down, on full it can take over 40A I believe).
Well we've never applied for a connection - it's been there when we moved in. We never go anywhere near the limit of the supply fuse (100A)When you or whoever originally applied for a connection to the DNO's distribution system, you declared what load you would want. The connection would then be provided to cater for that load. If you want to add additional load, you should ask to redeclare your load requirement. If you're unlucky some jobsworth will get hold of your request and charge you an arm and a leg to modify your connection.
You mean they'll do anything about that - a friend of mine has suffered from flickering lights for years and they won't do anything. Mind you, it's not local users causing it - no idea what is, but it's there all the time. All they'll do is plug a monitor in, declare the mains to be within spec, and leave. Done it for years, and IIRC (it's some time since he told me) it affects several houses in the street.An alternative is to add your load and keep schtum. You'll only run into a problem if a nearby consumer complains about his flickering lights.
The big black sticker on the fuse board answers your questions. I would of preferred if it said "Electrical equipment outside of the property".
Why would a permanently fixed air conditioning unit fed by SWA cable need an RCD? The fact that it is outside is irrelevant?
Hi
I will shortly be purchasing a split system with 1x outside unit and 2x inside units for my house (domestic).
The aircon company will do the refrigerant circuits and want the electrical circuits ready for when they arrive.
I will do as much of this as possible as well as employ a sparks and have some questions please.
Q1. For the external aircon unit I will need a separate circuit rated to 20A. My consumer unit is the old type with cartridge fuses. Do I need to upgrade the CU to a 17th edition complaint one with MCBs? If so I would get the sparks to do this!
Q2. Re. cable to external aircon unit, can I install Hi-Tuf or does it have to be SWA? I was going to use cleats to fix to outside of brick wall. Is this OK or do I need to use conduit and if so what spec please?
Q3. I did the Vd and EFLI calcs and 2.5sqmm will be fine however for belt and braces I will install 4sqmm. I was planning on doing the donkey work (routing the cable thru the walls) and leave the sparks to terminate the cable in the isolator/CU. Am I allowed to do this in terms of building regs?
Q4. Re. inside aircon units, I was advised by aircon firm that these units can be run off ring main circuits provided FCUs are used. Am I allowed to do this in terms of building regs? I've spurred off bedroom sockets in the past but never really knew if I was allowed to do it!
Thanks!!
PB