True. I agree that an N-E leak is definitely one of the possibilities, my only real point being that a significant N-E a leak (even if just a 'last straw') due to stray capacitance is next-to-impossible, assuming that the cables are not literally 'miles' long!Johnw2, true but firstly the RCD can operate at anything over half that, and depends what else is leaking on the same RCD.
Another thing which often goes unmentioned in these discussions about N-E leaks is that many (most?) circuits have at least some degree of L-E leak (due to filter capacitors in equipment etc.), and that will effectively subtract from any N-E leak, hence meaning that one needs more N-E leak than one might have expected in order to trip and RCD. In the worst case, with nearly 30mA of L-E leak, in simplistic terms (e.g. assuming that both leaks were resistive) it could take an N-E leak of anything up to 60mA (and certainly at least 45mA) to trip a 30mA RCD.
Kind Regards, John