Supposing a live conductor made contact with that internal copper piping? The only path to earth would be via the water in that section of plastic pipe.
What purpose does bonding a section of metal pipe serve, where the metal pipe disappears into the ground and is electrically completely isolated from an extensive metal pipe installation within a premises? Answer = none.
Water pipes themselves are not exposed-conductive-parts therefore do not require earthing.I would say that because the RCD should pick this up and trip.
If it's a pre RCD install though then yes you'd bond it.
It stops external voltages from being brought in to the house.
You will note that your linked article refers to extraneous-conductive-parts. That is the pipe in the ground earthed by the ground - The Earth - not the other pipe(s).
Isolated metal parts are not extraneous-c-ps and must not be bonded.
Only parts that are already earthed by some means need bonding to equalise any potential should a fault occur.
Earthing is not a good thing for its own sake; it is a necessary evil. It would be better if nothing required earthing but it is unavoidable for metal electrical equipment.
Your faulted reasoning also applies to metal door handles and the like which are not exposed-c-ps nor extraneous-c-ps.
Water pipes themselves are not exposed-conductive-parts therefore do not require earthing.
If they are connected to earthed appliances then they will be earthed by the appliance but it would be better if they were not.
Because they are earthed by an appliance they might require supplementary bonding in, for example, a bathroom.
This has nothing to do with Main Bonding which applies to extraneous-c-ps entering the premises.
No, there isn't.There is a world of difference between a metal door handle and a very extensive copper pipe system.
But that is a very much lesser hazard than all the pipes (and sink) becoming live because of an appliance fault - and grabbing the proverbial frayed flex while leaning on an earthed sink.Copper pipes commonly run under floors, usually mixed in with numerous cables and at risk of making contact with live conductors.
Exactly.I agree with your point about earthing being a necessary evil. My own home is of the era when every radiator, the entire metal work of the bathroom and all taps and metal sinks were carefully cross bonded.
Given that has never been required, which era was that?. My own home is of the era when every radiator, the entire metal work of the bathroom and all taps and metal sinks were carefully cross bonded.
Given that has never been required, which era was that?
That will be the era of late 70's/80's when the man with the company fuse and meter would test ALL exposed metalwork and if not bonded would not connect the supply. I did a lot of work for a builder and the chippies got very good at making routes in window sashes and frames to get a wire to the window hinges and handle.Given that has never been required, which era was that?
That will be the era of late 70's/80's when the man with the company fuse and meter
Does anyone know if there was a particular electrical guide / publication / union book or similar from then (1981) which actually covered bonding things like window frames and similar items?
The problem would seem to be one where someone has selectively read the regulations in the 15th edition, and taken a couple of items completely out of context.
Doesn't surprise me but as I mentioned 'No bonding = No power' by SEEBoards rules at least.We discovered recently when someone (Secure?) posted the regulations from way back then and the wording was virtually the same as it is now so - misinterpretation then as well.