In Line with Reg: 413-02-02 a Main Equipotential Bonding Conductor must be run to incoming services such as Water & Gas.
547-02-02 states this bond must be made within 600mm of Point of Entry to the building.
In TN-C-S Installations it has been noted that, occasionally, the voltage will rise on the Neutral/Earth Terminal above 0 volts.
This is not as much a problem as it may at first appear as the idea of the earth bonding is to ensure that there will be no potential DIFFERENCE between simultanious conductive parts within the installation thereby not presenting a shock hazard.
However, in the case of the incoming gas main, it is quite common for the pipe to run from an external meter for some distance outside the building before entering.
If the voltage did rise on the neutral/earth, this would be present on this external pipe and create a potential difference between the external pipe and ground.
This would be solved by installing an insulated section of gas pipe as it enters the building thereby effectively insulating the 'upstream pipe'.
Does anyone know if this IS a requirement and, if not, why not?
547-02-02 states this bond must be made within 600mm of Point of Entry to the building.
In TN-C-S Installations it has been noted that, occasionally, the voltage will rise on the Neutral/Earth Terminal above 0 volts.
This is not as much a problem as it may at first appear as the idea of the earth bonding is to ensure that there will be no potential DIFFERENCE between simultanious conductive parts within the installation thereby not presenting a shock hazard.
However, in the case of the incoming gas main, it is quite common for the pipe to run from an external meter for some distance outside the building before entering.
If the voltage did rise on the neutral/earth, this would be present on this external pipe and create a potential difference between the external pipe and ground.
This would be solved by installing an insulated section of gas pipe as it enters the building thereby effectively insulating the 'upstream pipe'.
Does anyone know if this IS a requirement and, if not, why not?