Following on from my previous thread, that has been zapped by Moderators, who only see me of using inappropriate language, I do not wind up people on here first, nor start offending anyone first, but if someone starts at me, and Moderators do nothing, I don't stand back and swallow insults. But I have learnt not to retaliate, but I will click on the post for moderators' attention. I will from now on use "report post" button.
Any ways, I found a novel way to figure out exact spot where a short circuit occurs in run of cable which may be buried under floor or under plaster.
1. First you measure the total run of the cable, one can guess how this cable must have run from a CU to its final termination point, measuring as accurately as possible, most cables runs would take a short logical and obvious paths. (Total cable length = TCL)
Once you have measured the length, irrelevant what units you use, metric or imperial
then get hold of a constant current power source, like 0 - 30V, 5amp current limited power supply. It must provide constant current.
2. Isolate cable at both CU and at the appliance end, unscrew wires from their terminations.
If the short is between say the live conductor to earth, then remove live conductor and its earth conductor which is likely where the short is between these two conductors.
3. Attach power source to the Live and earth conductor at the CU end and accurately measure the voltage as 5 amps flow through this shorted pair (E & L)
note this voltage reading. (V1)
4. Now do the same at the appliance end, feed 5 amp constant current and measure the voltage and note this voltage (V2)
from this formula below you can now work out exactly how far the short circuit fault is from either end i.e. CU end to fault (V1) or Appliance end to short circuit (V2)
Formula: Total Length of cable (TLC) divide it by voltage V1+V2 and multiply by voltage V1 to get distance from CU to fault or multiply by V2 to get distance from appliance end,
I tried this on a 7 meter 0.75mm cable and had a deliberate short at 2 meters from one end, and the results were astonishingly accurate to within a few inches of the fault.
I am going to use my technique to find out where that short is on that shower cable and hopefully we won't have to dig out the entire floor or rip plaster off the wall unnecessarily.
Any ways, I found a novel way to figure out exact spot where a short circuit occurs in run of cable which may be buried under floor or under plaster.
1. First you measure the total run of the cable, one can guess how this cable must have run from a CU to its final termination point, measuring as accurately as possible, most cables runs would take a short logical and obvious paths. (Total cable length = TCL)
Once you have measured the length, irrelevant what units you use, metric or imperial
then get hold of a constant current power source, like 0 - 30V, 5amp current limited power supply. It must provide constant current.
2. Isolate cable at both CU and at the appliance end, unscrew wires from their terminations.
If the short is between say the live conductor to earth, then remove live conductor and its earth conductor which is likely where the short is between these two conductors.
3. Attach power source to the Live and earth conductor at the CU end and accurately measure the voltage as 5 amps flow through this shorted pair (E & L)
note this voltage reading. (V1)
4. Now do the same at the appliance end, feed 5 amp constant current and measure the voltage and note this voltage (V2)
from this formula below you can now work out exactly how far the short circuit fault is from either end i.e. CU end to fault (V1) or Appliance end to short circuit (V2)
Formula: Total Length of cable (TLC) divide it by voltage V1+V2 and multiply by voltage V1 to get distance from CU to fault or multiply by V2 to get distance from appliance end,
I tried this on a 7 meter 0.75mm cable and had a deliberate short at 2 meters from one end, and the results were astonishingly accurate to within a few inches of the fault.
I am going to use my technique to find out where that short is on that shower cable and hopefully we won't have to dig out the entire floor or rip plaster off the wall unnecessarily.