to my mind there has never been a need for RCD protection of 8 volt door bell wires.
There is no need provided the wires never come into contact with mains voltage. If the door bell is supplied from batteries then RCD protection is not needed. There is a case to consider protecting a door bell when it's ELV is supplied by a transformer from the mains. Insulation / isolation failure in the transformer could raise the ELV to 230 volts above ground making a wet door bell push potentially lethal to someone touching it.
I favour earthing one side of the ELV such that insulation / isolation failure in the transformer will result in current to earth from the mains via the ELV wiring and this earth current would trip an RCD
That said the isolation in a transformer with primary and secondary separated on split or dual bobbins is very unlikely to fail. Single bobbin transformers with primary and secondary windings separated only by a layer of tape insulation can fail.