So, if I understand correctly, for an uncontrolled ring final, assuming a CCC of 20A and an MCB of 30A, you would want the sockets to be in the middle 1/3 of the cabling...
That's about the size of it. Because you can't be sure what will get plugged into which sockets, the only way you can ensure a reasonable load distribution is by avoiding clusters of sockets close to the start/end of your ring.
With my hypothetical quad-pole RCBO, there is no need to make the design "uneconomical" as both ends of the ring can supply at least 20A (which is suitable for living rooms) and the middle of the ring can supply up to 40A (which is suitable for kitchens).
So, you propose a circuit design which now requires people to understand what load they can attach, depending on the geography of your socket layout. I think you'll find that users are neither interested, nor capable of understanding this concept.
1. OK, with your 'centre 1/3' rule as I have inferred. But it frees designers of that constraint and/or the assumption of even distribution.
No it doesn't. it means designers and installers will have to guess where the bigger loads might be concurrently applied and you could end up with some very interesting cable routes.
It completely eliminates the possibility of localised load overloading a single cable.
At the expense of a level of complexity which is neither sensible nor required - because a radial socket-outlet circuit will already do the job without any special rules for how the circuit is used.
It also protects the cable in case of a continuity failure.
By converting a strange kind of a ring into a lower-rated radial.
An MCB (or just 'circuit breaker' as they have been called by the British Standard for almost twenty years) only directly protects the live (line) conductor(s), my suggestion protects all 4 live and neutral conductors (neutral is a live conductor, by definition) - isolating the whole ring final on any overload.
Single-pole isolation is both safe and normal, but if you want to isolate
both live conductors - that's line and neutral - feel free to procure a caravan consumer unit.
2. Actually, without your 'centre 1/3' rule, there will be cable savings...
No. Rings always use more cable than you would use if you supplied the same demand through radial circuits. That's one of the things they
really got wrong back in 1947.
(There will always be good reasons to separate circuits but I don't think that load distribution on a ring final should be one of those reasons.)
Quite right. If you read Reg 314.1 you will see that rings are not even mentioned. This still does not mean that a ring final circuit should be the automatic choice for socket-outlets.
...I am suggesting a circuit protection that is easier to design with...
No, you're not. Keep it simple. Rings are not only
not simple, they are fundamentally flawed in design, poorly installed, rarely tested and are only tolerated by the use of a 'deemed to comply' regulation which almost nobody seems to follow.
I do follow your argument, by the way, but you are trying to solve a problem which need not exist.
And given that I teach electricians for a living (not children, by the way, grown-up, already qualified, adult electricians, from a wide range of backgrounds) I can assure you that the proportion of sparks that would understand what you are suggesting is very low indeed.