Went to put in a new cooker supply for a customer yesterday. Just doing a couple of quick checks before I got started and found the incomming supply to have a Ze of 11.40Ω on a TN-S
Good old cast iron cut outs
Anyway the nice chaps from northern powergrid came out and got the reading down to 0.31Ω
Aparrently the supply was looped off next door and both cables in their house and the cable in the one I was working in all had the earth clamps onto the cable armouring rather than the lead sheath.
I guess I'm the first person who's ever actually used a test kit in either of these houses then
Good old cast iron cut outs
Anyway the nice chaps from northern powergrid came out and got the reading down to 0.31Ω
Aparrently the supply was looped off next door and both cables in their house and the cable in the one I was working in all had the earth clamps onto the cable armouring rather than the lead sheath.
I guess I'm the first person who's ever actually used a test kit in either of these houses then