diablo1952 said:* Can someone explain why the main switch trips and not the individual circuit breakers!!!!!!
It is not a main switch; it is an RCD (which can be used as a main switch but this is not the best design).
By "Individual Circuit Breaker" you mean an MCB. An MCB will be marked "B6" B16" B32" etc. that means it is designed to support a circuit carrying a max load of 6Amps, or 16 amps, or 32Amps. Loads above this will cause the MCB to trip. The greater the overload, the faster it will trip. A short circuit will make it trip very fast.
An RCD is not an Overload device. It is usually rated "30mA" or sometimes "100mA" (other ratings are available for different purposes). That means that if it detects an earth fault of 30 milliamps, or of 100 milliamps respectively, it will cut all power passing through it, usually within 0.03 of a second or less. this is fast enough to prevent you being injured or killed by such a fault.
The fault arising in the thread is an Earth Leakage Fault. This can be caused by e.g. water getting onto connections; or a faulty appliance, or a mouse gnawing a live cable, or someone touching a damaged cable.