The earthing looks like PME, as it emerges from the side of the service fuse holder block - where is the lower half of the service fuse holder block? - the lower half normally covers up the unsightly incoming cables.
A bit of a conflict there.....I HATE gas with a passion. I know for hob it is the best.
A bit of a conflict there.....I HATE gas with a passion. I know for hob it is the best.
Even though YOU KNOW that gas is better.I would have induction any day over gas.
where is the lower half of the service fuse holder block? - the lower half normally covers up the unsightly incoming cables.
Even though YOU KNOW that gas is better.I would have induction any day over gas.
The earth cable would be upgraded when your spark does the CU change. It is supposed to be 16mm² for a PME (TNC-S) supply.
The PME earthing terminal shall not be made available to the customer unless:
11.3.1 A main equipotential bond of not less than the copper equivalent area shown in Table 2 is installed to bond the incoming metallic gas and water services to the customers’ protective conductors; and
11.3.2 Other exposed metalwork in the premises which is directly connected to or in contact with metalwork buried in the ground is also bonded to the PME earth terminal using conductors of size as detailed in Table 2. Note that such bonds are also main equipotential bonds; and that telecommunication cables are exempt from the requirements of this paragraph 11.3.2.
The method of bonding gas service pipes to customer’s earth terminals shall be in
accordance with the BS7671. Figure C3 in Appendix C shows an example of such bonding.
TABLE 2
Copper equivalent cross section of **** service neutral conductor/
Minimum copper equivalent cross section of main equipotential bonding conductors
not greater than 35mm2/10mm2
over 35mm2 to 50mm2/16mm2
over 50 mm2 to 95mm2/25mm2
over 95mm2 to 150mm235mm2
over 150mm2/50mm2
I think you'll find it's called the Earthing Conductor. With PME, 542.3.1 requires that it is sized as per the the MBP conductor (i.e. as specified in 544.1.1 and its Table 54.8 ). I can see no explicit indication that one can go below those sizes (for either MPB or Earthing Conductor, with PME) by using adiabatic equation calculations.The adiabatic equation is only used for cpc's, but what is the cable called between the MET and the service head. If its a cpc you could be correct, if its a bonding conductor you're wrong.
As above, I don't see any indication that use of an adiabatic equation is allowed - and, in any event, 542.3.1 prevents the Earthing Conductor from being smaller than the MPB conducor with PME,Using the adiabatic equation, you could end up with a main cpc smaller than the main bonding conductors, that can't be right.
It could have been sized with the adiabatic equation,
I think you have found another anomoly in the regs. The adiabatic equation is only used for cpc's, but what is the cable called between the MET and the service head. If its a cpc you could be correct, if its a bonding conductor you're wrong.
Using the adiabatic equation, you could end up with a main cpc smaller than the main bonding conductors, that can't be right.
A bit of a conflict there.....I HATE gas with a passion. I know for hob it is the best.
Not really, I do not want gas, it's quite easy, everyone says gas is best for hob, but I would have induction any day over gas.
Anyway dont see what that matters, seems I need to get onto DNO and the sparks when I move in end of this month.
Cheers
So is the earth cable undersized? It is a MAX of 6mm, no way is it 10mm, I would say the tales are 16mm to the Hendly blocks, then 25mm to the CU.
Cheers