So what do you call the load cable/circuit connected to it?
The 'appliance'. or "load" as you called it
DS
So what do you call the load cable/circuit connected to it?
No, what do you call the cable/circuit?
You can't use a plug top. You can however use a complete plug.Mm, is that a fuse supplying that "spur"? Would that be a "fused spur" ? Oh, lets add a switch.
That would be a switched- fused- spur ideal if you don't want to use a "plug top" !
DS
There is a fuse; it is protecting the spur.Mm, is that a fuse supplying that "spur"?
No, the cable is the fused spur.Would that be a "fused spur" ?
No, the cable is the switched fused spur.Oh, lets add a switch.
That would be a switched- fused- spur
As Winston's reply above.ideal if you don't want to use a "plug top" !
So, you are just being silly.yes, you've got it !
As you say, not likely.Not likely to be an issue on a 32a ring with 13a plug fuses, but other situations may happen.
True not many, but not everyone is a fan of rings, some people prefer 20a radials, maybe you have a 16a or 20a radial from your cu at the front to your garage at the back on 1.5mm cable, or maybe a 13a fcu supplying the garage from another final circuit, then you plug a 25m extension into that to get to your shed (that's what next door does although off the ring) then a lamp and a laptop plugged in.As you say, not likely.
25m of 1mm² flex is needed to increase max. Zs of the ring to max. Zs of 13A fuse.
How many sockets are already at maximum Zs?
"Extension lead fires" will only result from overload of the extension cable (bearing in mind the maximum safe current when wound or not wound in the case of extension reels), and that ought to be covered by the fuse in the extension lead plug. The 'maximum Zs' business is all about (negligible impedance) 'faults', not overloads, and they are very unlikely to start a fire in the cable before some protective device operates.As we both say, all very far fetched, but it's interesting that ordinary people can effectively design arbitrary circuits using extension leads. .... But presumably in amendment 3 the worry was cu fires not extension lead fires, so it's probably not worth effort.
Yes assuming the zs is low enough. The situation under discussion is where the zs to the end of the lead is too high for the 13a fuse in the plug. Then a fault (to earth) would not be cleared in time. I suppose that's more about the shock risk than a fire, so just hope there's no extraneous metallic parts nearby. All very unlikely, but it doesn't give eebads so wouldn't comply with the regs if it were fixed wiring.The 'maximum Zs' business is all about (negligible impedance) 'faults', not overloads, and they are very unlikely to start a fire in the cable before some protective device operates.