Very good question - you tell me! I've seen "6A" ones as well.It would be half a job if they stopped selling those 10A rated extension leads, where did that stupidity start from?
Kind Regards, John
Very good question - you tell me! I've seen "6A" ones as well.It would be half a job if they stopped selling those 10A rated extension leads, where did that stupidity start from?
That's what I said/implied. However ....Yes assuming the zs is low enough. The situation under discussion is where the zs to the end of the lead is too high for the 13a fuse in the plug. Then a fault (to earth) would not be cleared in time. I suppose that's more about the shock risk than a fire ....
I don't think the arithmetic supports the feasibility of the scenario you are postulating ... to get 0.4s disconnection time (i.e. assuming TN installation), a 13A BS1362 fuse requires a current of about 36A. With a Cmin of 0.95, that equates to a max Zs at the end of the extension lead of about 6.07Ω. Assuming the extension lead is fed from the 'highest Zs socket' on a circuit protected by a B32, which has just a low enough Zs (i.e. 1.37Ω), that means that the maximum (R1+R2) at the end of the extension cable (max for EEBADS) would be about 4.70Ω (6.07Ω - 1.37Ω) - which, if the extension cable were 1.25mm² flex, would equate to a maximum permissible extension lead length (max for EEBADS) of about 127 metres - longer than any extension lead I can recall having encountered!... All very unlikely, but it doesn't give eebads so wouldn't comply with the regs if it were fixed wiring.
so I can't plug my fan heater in on the moon after allextension lead length (max for EEBADS) of about 127 metres
Indeed, but I think it's probably reasonable to consider probable modes of 'wrong use' and, where possible, take steps to minimise the risks.I suppose one can buy all sorts of things which are unsuitable when wrongly used.
I suspect that 'limitation' probably resulted from the fact that it was not intended, nor considered appropriate, that BS1363 plugs/sockets should be used to connect loads greater than 3kW ... it's probably not just a coincidence that the plugs, sockets and fuses were designed for a max current of 13A.Maybe that's why standard plug fuses are limited in comparison with your average socket circuit
So it does (I've never noticed 1362's in that table before!). However ...According to Table 41.2, .... the maximum Zs for a 13A 1362 is 2.3Ω.
The Table 41.2 max Zs of 2.3 for a 13A BS1362 implies that, at (0.95 x 230V), one would require a current of 95A to guarantee disconnection in 0.4sec. That is so close to the current required to guarantee disconnection by a B32 in 0.4s (i.e. 100A) that one could not have hardly any length of extension lead if the Zs at the supplying socket was already 'on the borderline' (unlikley, see below) and there were a requirement (which there isn't) to satisfy the disconnection requirements at the end of the extension.So with a marginal 20a radial rather then a 32a ring you couldn't even use a 25m extension!
I have leads right down to 0.5mm² to limit the weight and size but their use is carefully controlled.Very good question - you tell me! I've seen "6A" ones as well.
Kind Regards, John
I have 100m leads but in 2.5mm² & 6mm² but using things that long are not a walk in the park [actually that's the sort of place they would be used and a lot of walking is involved with long cable runs] always have to do the tests and calcs to work out what size MCB's to use and sometimes we're down to 4A for a long 6mm² run., if the extension cable were 1.25mm² flex, would equate to a maximum permissible extension lead length (max for EEBADS) of about 127 metres - longer than any extension lead I can recall having encountered!
KInd Regards, John
Fair enough, but don't forget that my "127m" calculation was 'incorrect' (for a worst-case-scenario calculation) - it should have been nearer to 25m (per my subsequent post).I have 100m leads but in 2.5mm² & 6mm² but using things that long are not a walk in the park ... always have to do the tests and calcs to work out what size MCB's to use and sometimes we're down to 4A for a long 6mm² run.
Indeed, but the manufacturers are not blameless, since they give no guidance/warnings with long extension leads. I have a couple of 50m reels ones, and neither says anything about their use, other than that they should be fully unwound if used to their 'full capacity'.Then I see several domestic caddies used to power a tea urn, or worse, a tea urn and a kettle as the urn takes so long. The public generally have no clue when it comes to mains cables.