Good morning all. Help required!
I've just had an Intergas OV30 Boiler installed by STL Heating. We have 13 rads in the house with 7 TRVs fitted. We cannot put the heating on or control the house temperature at all as the system was not balanced. We now have no Hot water so had to get a Corgi Registered Gas Engineer out. These were his observations of a poor installation, and he has asked for circa £850 to fix it;
1/ Insecure Flue. It needs to be screwed not a push Fit.
2/ Not enough TRV's added. 3 more need adding and 1 removed from the Hallway where the Thermostat is.
3/ Outflow temp is 76 deg, Inflow Temp is 70 Deg. This was signed off by the STL Heating Engineer. Return feed needs to be sub 55 Deg so the Condensing Boiler can actually condense.
4/ Addition of final TRV's will allow the system to balance. Balancing of the system was never done and could not be without the additional TRV's being added.
5/ 3 way valve Broken. (Not picked up on the installation). Replace valve and controller
6/ Re-add Central heating inhibitor.
Can anybody give me an honest answer to get this lot sorted please?
Many Thanks
I've just had an Intergas OV30 Boiler installed by STL Heating. We have 13 rads in the house with 7 TRVs fitted. We cannot put the heating on or control the house temperature at all as the system was not balanced. We now have no Hot water so had to get a Corgi Registered Gas Engineer out. These were his observations of a poor installation, and he has asked for circa £850 to fix it;
1/ Insecure Flue. It needs to be screwed not a push Fit.
2/ Not enough TRV's added. 3 more need adding and 1 removed from the Hallway where the Thermostat is.
3/ Outflow temp is 76 deg, Inflow Temp is 70 Deg. This was signed off by the STL Heating Engineer. Return feed needs to be sub 55 Deg so the Condensing Boiler can actually condense.
4/ Addition of final TRV's will allow the system to balance. Balancing of the system was never done and could not be without the additional TRV's being added.
5/ 3 way valve Broken. (Not picked up on the installation). Replace valve and controller
6/ Re-add Central heating inhibitor.
Can anybody give me an honest answer to get this lot sorted please?