I do like
@stem idea of putting pump on plug and socket.
The other problem is how long it can take to trip, it can easily run fine for 10, 12, 15 hours then randomly trip, doesn't seem to matter how much load there is either...
This is the problem I had with old house, never could put my finger on why it tripped. All sorts of ideas, but no real way to prove it.
In around 1992 I returned from working in the Falklands, until then the ELCB as it was then called, was a rare beast only used with TT (earth rod) installations, the IEE wiring regulations had just been made into a British Standard BS 7671:1992 and there seemed to be a shift onto safer systems, and Sizewell 'B' seemed to be full of the ELCB, RCCD, or RCD which ever name you like, and they were a huge problem, in the main due to not switching neutrals, so some thing switched off, was not isolated, so a neutral to earth fault could still trip the RCD even when switched off.
The other was lack of discrimination, we would have a 5 amp and 5 seconds RCD feeding a 1 amp at 1 second, feeding a 100 mA type S feeding a 30 mA at 40 mS and some one would cause an earth fault and every RCD would trip, some times it would only take the 30 mA one out, but also would have them all trip together.
I had a workshop with a 10 mA MK metal clad socket, and pressing the test button would also trip the 100 mA one in the main board.
However over the years they do seem to have improved, and they don't trip as easy, however still loads of the old ones around, today the 30 mA RCD is sold as four main types, the type AC
should have the single sine wave sign, my old ones don't have any sign, it seems type AC can be frozen by DC so today we tend to use type A
these can stand 6 mA of DC, and there are other devices to detect the DC so if there is DC the other device will trip, then we have the high frequency
where we are using switch mode power supplies we can get high frequency, personally never fitted one, and not seen a RCBO as type F or for that matter type B which is next in the list type B
are used with EV charging points and solar panels and will work with over 6 mA DC out of interest which type do you have?