Extremely vague, and doesn't really seem to preclude a brick-built enclosure (as has been implied, probably closer to 'non-combustible' than metal!).Not really. See the definition of enclosure.
Kind Regards, John
Extremely vague, and doesn't really seem to preclude a brick-built enclosure (as has been implied, probably closer to 'non-combustible' than metal!).Not really. See the definition of enclosure.
Probably would. Know anyone who has performed the tests?It provides double and/or reinforced protection if you close the doors and windows (except that the front door lock bridges that protection, but then these fittings are isolated from hazardous parts by the appropriate clearance and creep-age). I'm quite confident that a double cavity brick wall, a double glased window would for each element meet the requirements for single insulation, and that a UPVC window frame or door would also provide reinforced insulation if tested.
I think you're confusing 'enclosure' with 'enclosed electrical operating area'.A house could also be an enclosure, as long as you didn't let non-competent people in it.
It was mrstitt, not me, who talked about houses. I was merely talking about a brick-built enclosure (one assumes with some sort of access door!) - which I would think could provide basic protection.How does a house provide basic protection? Or don't you know what that means either?
Well, if you're going to claim compliance with BS7671, then the enclosure would have to meet that definition, so it would have to provide basic protection, although I agree that would then be two layers of basic protection.In any event, in context, despite the BS7671 definition of an "enclosure", I'm not sure that such a 'secondary enclosure' would necessarily have to provide basic protection, would it (if the enclosure of the plastic CU within were already providing basic protection)?
I think you're confusing 'enclosure' with 'enclosed electrical operating area'.
I'm not sure that such a 'secondary enclosure' would necessarily have to provide basic protection, would it (if the enclosure of the plastic CU within were already providing basic protection)?
Since we're getting fairly pedantic .... I've just noticed something we've overlooked. We've been talking as if 421.1.201 just says that a plastic CU may be enclosed in "an enclosure constructed of non-combustible material..." (thereby theoretically invoking the BS7671 definition of "enclosure", which requires that it affords basic protection). However, what it actually says is "a cabinet or enclosure", so that (in the absence of a BS7671 definition of "cabinet") a brick-built cabinet with a 'non-combustible door" (whatever that might be) would presumably not be required to afford basic protection (although it would).Well, if you're going to claim compliance with BS7671, then the enclosure would have to meet that definition, so it would have to provide basic protection, although I agree that would then be two layers of basic protection.
Eh?all plastic enclosures provide reinforced insulation.
Yes, so all we need is a non-porous, non-brittle ceramic material and we can make compliant consumer units! I wonder if NASA have any left of those tiles they used on the space shuttle?
Indeed - but it was stillp, not me, who (I would say rather pedantically) raised the point that any mention of "enclosure" within BS7671 must be taken to imply the definition of that word as given in Part 2 of BS7671 - which definition requires that the (secondary) enclosure provides basic protection.The additional requirement in amendment 3 requires an enclosure that is non combustible. No mention of electrical safety whatsoever.
Good point! There is an IEC definition though:In any event, as I've just written to stillp, we are apparently allowed to put our plastic CU in a cabinet, rather than an enclosure, if we so wish - and that does not invoke any BS7671 definition