It might, if the Honeywell had a terminal 5!here is the old honeywell, brown was in t 1 (top right), blue t 5. Does this help to solve?
It might, if the Honeywell had a terminal 5!here is the old honeywell, brown was in t 1 (top right), blue t 5. Does this help to solve?
What terminals were the wires connected to in the Honeywell - it is important to use the numbers actually marked on the unit.Random, the instructions do not mention using terminal 3. Just neutral to 4 and connecting to mains which it seems to suggest to 1 on the diagram? Maybe the blue is permanent live.
Your old Honeywell did not have a neutral connection.the honeywell had brown in t1 (top right) and blue t3 (not 5).
you have a live and a switched live
Just because the wire is blue, doesn’t make it a neutral wire.
Instead of using terminals one and four, you need to use one and three.
M just denotes the load to be powered, it could be a boiler, or a 'M'otorised valve, pump, etc.What is the "M" in the greenbrook instructions?
Yes, but in this case, as there are only two wires, it doesn't really matter which goes into 1, or 3!Thank you. So is the brown likely to be the permanent live? - This to 1? Switched live to 3? I can voltage test each wire.
You see the big rectangular block after terminal 3 - this again represents the load to be powered.The Honeywell is saying N by terminals 2 and 3, can you explain what these N's signify?
Yes, there will be no light, unless you rewire it with a neutral.operate the light, does this mean I will not have the light come on?