hi there all I have 2 queries to ask so i'm hoping you'll go easy on me as it is my first post and also my first two jobs which are also for the niceic assesment.
My first is a high Ze result on a TT system which has a reading of 353 ohms for which I nearly had a fit because I had only just upgraded his main earthing conductor to 16mm from what looked like a piece of earth cable from a flex.A little birdie told me that the electrode may not be conducting because of it being too dry in it's hole and to soak the patch in which it resides with water,anyone heard of this or am I just better off buying a new electrode for him and placing it by the side of the old one?
My second is a garage installation which is set 47m away from the main house.Again a TT system is installed with a BS1361 60A distributor cut out,a BS4293 30mA rcd main breaker an 8 way cu with no spare mcb's.What I have done is installed a 40A 30ma rcd in the garage with a 32A and 6A mcb's and supplied the garage cu from the house using three core 6.0mm swa to avoid the volt drop.In the house because there was no spare mcb's and to avoid discrimination between the 2 rcd's i've placed a 63A main switch isolator between the 6.0mm swa and the incoming side of the BS4293 rcd breaker in the house' cu and has also been wired using 6.0mm.All test results are good with only one exception and that being the Zs of the two circuits in the garage which is extremely high at 17.65 ohms compared to that of tn-s and tn-c-s systems which are valued a lot lower.Is this to be expected for this type of system as I have never tested a TT system before and the only test we done on the part p course was on a tn-s system.
Any thoughts or critisiscm is welcomed as i really don't want to screw up this assesment and many thanks to all for their time taken to reply to these queries.
djjd21
My first is a high Ze result on a TT system which has a reading of 353 ohms for which I nearly had a fit because I had only just upgraded his main earthing conductor to 16mm from what looked like a piece of earth cable from a flex.A little birdie told me that the electrode may not be conducting because of it being too dry in it's hole and to soak the patch in which it resides with water,anyone heard of this or am I just better off buying a new electrode for him and placing it by the side of the old one?
My second is a garage installation which is set 47m away from the main house.Again a TT system is installed with a BS1361 60A distributor cut out,a BS4293 30mA rcd main breaker an 8 way cu with no spare mcb's.What I have done is installed a 40A 30ma rcd in the garage with a 32A and 6A mcb's and supplied the garage cu from the house using three core 6.0mm swa to avoid the volt drop.In the house because there was no spare mcb's and to avoid discrimination between the 2 rcd's i've placed a 63A main switch isolator between the 6.0mm swa and the incoming side of the BS4293 rcd breaker in the house' cu and has also been wired using 6.0mm.All test results are good with only one exception and that being the Zs of the two circuits in the garage which is extremely high at 17.65 ohms compared to that of tn-s and tn-c-s systems which are valued a lot lower.Is this to be expected for this type of system as I have never tested a TT system before and the only test we done on the part p course was on a tn-s system.
Any thoughts or critisiscm is welcomed as i really don't want to screw up this assesment and many thanks to all for their time taken to reply to these queries.
djjd21