in answer to flameports reply i used 3 core swa to take both phase conductors and an earth to the garages own cu unit which consists of a 40A,30ma rcd 1no 32Amcb for a 6 outlet ring main and a 6Amcb for the lighting does this not class as overcurrent protection.the isolator has been put in place just to cut the power to the garage consumer unit.
You need overcurrent protection for the swa from the house to the garage , which the isolator doesnt give.
Out of interest what csa are the P/N/E tails from the supply into your 63amp mainswitch & how have you gone about connecting it?
I tend to split the meter tails with henleys, take a set of 25mm tails into an enclosure containing dp 100A mainswitch & a correctly rated mcb these then supply the sub to outbuilding.
in answer to desl question the (r1 + r2) test in the garage was 0.17ohms for the ring circuit and 0.56 ohms for the lighting circuit and the Ze at the electrode at the front of the house is 76.3ohms
And what was the Zdb / R1+R2 / IR of the submain ?
If you've installed it, you need to test & cert it.
A little birdie told me that the electrode may not be conducting because of it being too dry in it's hole and to soak the patch in which it resides with water,anyone heard of this
Correct it's call soil conditioning, but adding another rod is the better method.
upgraded his main earthing conductor to 16mm
Doesnt need to be 16mm, could be as small as 2.5mm.........dont they teach this on the 7 day course?
my course was 7 days in total and i'm planning on the 17th edition exam early in the new year.
Get you money back 7 days aint long enough & be prepared to pay for a re-assessment.
It's not your fault it's these colleges & such places that give the impression that after 7 days reading about it you will be free to call yourself an electrician & do the work associated with being one.
and the only test we done on the part p course was on a tn-s system.
And there you have it.......grab your cash then teach the bare minimum.