I did as you asked and the D.0 reading appears as 30
d.0 is the heating part load in kW. If it is 30, then the boiler is set to max output.
Is the normal for a Valiant Eco Tec Plus 428 heating 11 Rad, 4 bed detached house fully insulated both wall and loft?
I have a similar sized house to you with 13 rads and full wall and loft insulation. The boiler is 15kW.
You need to range rate your boiler down to about 15 or 16kW
Use the Boiler sizing wizard in my previous post to find out what size boiler you should have bought. Use this as a starting point for adjusting the boiler output.
• Press the “i” and “+” buttons simultaneously.
• Keep the “+” button pressed until “d.0” is displayed.
Note: The display runs from “d.0” to “d.99” before restarting at “d.0”.
• Press the “i” button. The “=” symbol is displayed. The part load setting is now displayed in kW.
• Use the “+” and “–” buttons to increase or decrease the value in steps of 1 kW. The displayed value will flash while the adjustment procedure is being carried out.
• Push the “i” button for about five seconds, or until the display stops flashing. The value is now saved to memory.
The display will now return to its normal state (current heating system flow temperature, e.g. 45 °C).
• Press the “i” and “+” buttons simultaneously to cancel
adjustment mode.
Adjustment mode is also cancelled if no button is operated for a period of 4 minutes.