davelx said:
The thing that makes no sense here is that if the hob+oven were combined in a single unit, i.e. a cooker, then the diversity calculation would give a lower current rating, even though both cases are identical from an electrical load standpoint.
Diversity is supposed to be applied bearing in mind how the circuits and appliances are used, not by blind adherence to the formulae. It makes no sense to me at all to treat a separate oven and hob any differently from a free-standing cooker that combines the two, since the two are used in the same way (how many sparks actually USE these appliances in anger, I wonder - I do).
If you treat them this way, then even with the 5A for the socket, the load is 26.4A and your 32A MCB is OK.
I guess there might be some argument for the ability to isolate the two appliances independently, but that is the only reason I can see for separate circuits.
There are two reasons for connecting the two appliances seperatly:-
1. Isolation of each seperatly
2. The Flex for any appliance is only rated for the load of that appliance
so for the double oven the flex is only rated at 19A. You can not
connect this cable to a circuit which is protected by a 32A Breaker.
Same for the Hob. So connect the Hob(29A) to the Cooker outlet and
Oven on a 13A Plug.