Indeed - and, whilst it may be £100+VAT in Wales, recently heard from someone (in England) whose LABC was asking for £500+VAT.
I saw that post, and not convinced those were really the LABC charges, the idea was in England to allow each local authority to set their own fees so to reduce the charges for Part P work.
However in Wales the £100 plus vat does not include the cost of third party inspectors, so if the LABC employ an electrician to do an EICR then the home owner is charged for that on top of the standard fee.
230/(32x5)x95% = 1.365625 Ω but most of the cheap (£50) plug in testers pass at 1.9 Ω so unless the DIY guy has test results of the original installation he has no idea if adding more cable will stop the overload from tripping within the required time.
When I first started the meters and regulation books where kept in the foreman's office, and we were discouraged from using them, but when BS 7671 came in, we started using the meters, and completing the installation certificates, and I was shocked to find out how many large houses were not within the requirements which did not have the 5% safety margin then so 1.44 Ω if using 240 volt the 1.5 Ω, so even if originally within spec, with the volt drop and 5% safety margin could be out of spec now.
The MCB was the real problem, with a fuse a little too much cable would just take a little longer to open, but with the MCB if the magnetic bit does not trip, one is looking at a massive increase in time before the thermal part will trip.