Hi again – here’s an update after a month spent trying to get our plumber to look at resolving the intermittent, but at least daily, bangs/thuds/dunks from our unvented central heating system.
...this time with photos after dissembling the airing cupboard to get better access!
In short, is there anything we can do without having to drain the system? Otherwise, suggestions were to replace two-port valve that appears to make the noise and/or convert from Y-plan to S-plan by ditching the three-port?
I’ve tried to summarise where we got to at the start of November, where we isolated the issue down the DHW two-port valve opening after the CH has been running for some time. We can reliably re-create the effect by forcing open the DHW two-port valve, both manually & by adjusting the cylinder stat down to call for HW, regardless of whether the CH is currently running but *only* after the CH has been running for some hours after the DHW valve closes. I found we can alleviate the noise by powering off the system at the mains which allows the three-port to return to its rest and noiselessly seems to relieve the pressure that appears to build up when the CH runs.
The existing Y-plan system had these new components added/replaced:
* Vaillant ecoFIT pure 415 heat-only gas boiler & control unit with wireless control panel & external temp sensor (replacing a Baxi Solo PF3)
* Wilo multi-mode pump running at ~5-8 cubic meters/hour in “c1” (replacing a Grundfos)
* Spirovent de-aereator between the pump & three-port (new)
* Magnetic particle filter next to the boiler (new)
* Honeywell NC two-port safety vale on the DHW flow pipe (like-for-like replacement of 20yo part)
* Heating circuit expansion vessel in the loft (replacement)
* Hot water circuit expansion vessel also in the loft (new addition to Megaflo)
And leaving these original/older components:
* Megaflo unvented 200 litre cylinder (20yo but not showing any signs of failing)
* Honeywell three-port (replaced in 2021)
* Califei air valves by boiler flow & DHW (replaced 2021)
* Cold water feed pressure control valve (replaced early 2024)
* 14 radiators over three floors with all copper piping
Looking back at questions that were posed and we maybe didn’t answer clearly.
Madrab
>It may be easier to take it back to basics, remove the 3 port, introduce a NO on the CH side and standardise the wiring as a PDHW system.
Essentially we do currently have PDHW, as the system only does CH at 30-50 Celcius, or DHW at ~70. Just not as quietly as we would wish it.
Johntheo5
Key point you made:
> If the MPV is staying in its "last port of call", say after CH mode above, then the water will be trapped between the MPV and the 2 port so just maybe building up a bit of pressure due to heat or whatever?
The DHW activation sequence opens the two-port before the MPV moves between A/B...so the pressure is arising between the valves. Wonder if we can provoke it by opening the MPV?
...and the answer is “no” it seems to quietly release the pressure, after which the two-port opening is uneventful.
>Have you any wiring diagram for this setup?
It seems pretty normal in the picture, but we haven’t deciphered all the bits
> So can you confirm (again?) that if DHW reheat was last requested and then subsequently requested again then no noise
Yes, that’s what happens, as long as the CH isn’t running for long between times
>Can you manually vent that Spirovent?
Not that we’ve found a way
dilalio
> And perhaps a sketch of the installation
See photos – can produce a schematic over the weekend if useful
>I'd suggest ensuring the pipework is properly secured as a start
Mostly the pipes are well fixed, but the system didn’t suffer this problem before the new boiler went in and the additional pipes aren’t particularly loose