taxes your going way over the top. sounding like a student thats just passed all his reg courses.
Hi,
You could not be more wrong but I see no point in arguing with you.
The following is an extract from one water authority's byelaws:
"Topic B22 states -
“Heating system appliances of any size in purely domestic premises, and single appliances or combinations of appliances rated at an output of not more than 45kW (150,000 Btu/hr) in other types of premises (such as small offices), should be regarded as a fluid category three backflow risk. For such appliances, a temporary filling loop with a double check valve for backflow protection is permitted, the filling loop being disconnected when it is not in use. The double check valve must be installed before the filling loop and remain on supply pipe connection when the loop is disconnected. For appliances above this heating output, in other than a house, the filling system would require fluid category four protection.”
It is not for me, nor you, to say that the rules should be ignored. We HAVE to obey them.
The Worcester device is NOT a temporary fitting, is not disconnected when not in use and is not a check valve. It does not prevent backflow if the boiler pressure at the time of attempted filling is higher than the mains supply. Highly unlikely I know, but that is precisely what the water authorities are trying to guard against. This guy is worried about possible contamination of his drinking water and the simple fitting of a non return valve will remove all such possibility.