Had a builder do the shell/structure of my loft conversion earlier this year and I'm DIYing the rest.
Whilst putting insulation in I've discovered he hasn't left ventilation at either end of the cold dormer roof. It's felt on top, with 150mm (145mm) ceiling joists, plus firrings. Am using 120mm Celotex in between joists, with 25mm Celotex underneath. Taking the firrings and 120mm Celotex into account, the ventilation gap (between top of insulation and bottom of roof OSB) spans from 63mm at one end to 33mm the other end - I know, a little less than the recommended 50mm ventilation gap, but that particular detail is the least of my worries at the moment! Because...
I've already discovered severe condensation when I removed one of the roof insulation boards and found the dormer roof OSB wet to the touch! The top of the ridge beam is also wet to the touch.
I know it will be (relatively) easy enough to vent at the far end of the dormer roof - using soffit or fascia vents. However I know I need the air to circulate i.e. vented at both the 'far' dormer soffit end, as well as the ridge end. Am toying with the idea of mushroom vents on top of the dormer roof, but there are 13 openings and obviously I don't want 13 mushroom vents on my dormer roof! (would need one for each opening as there's currently no way for the air to circulate between them)
I'm also thinking I could notch and drill holes in each and every joist to the maximum regulations permitted, that would create some sort of airflow in between joists, and possibly result in needing far less mushroom vents? (could I get away with just 3 - one in the middle and one at each end?) I've attached a diagram showing joist holes and notches I've calculated. I'd have to batten 44mm x 44mm timber to the bottoms of the joists and bring the 120mm Celotex down to that level to allow for 30mm holes to still have the required 50mm height clearance from the hole to the top of the joist.
Also concerned about the roof leaking if I get a roofer to put mushroom vents into a felt roof, whether it's 1, 3 or 14...
Any other solutions to provide ventilation?
Whilst putting insulation in I've discovered he hasn't left ventilation at either end of the cold dormer roof. It's felt on top, with 150mm (145mm) ceiling joists, plus firrings. Am using 120mm Celotex in between joists, with 25mm Celotex underneath. Taking the firrings and 120mm Celotex into account, the ventilation gap (between top of insulation and bottom of roof OSB) spans from 63mm at one end to 33mm the other end - I know, a little less than the recommended 50mm ventilation gap, but that particular detail is the least of my worries at the moment! Because...
I've already discovered severe condensation when I removed one of the roof insulation boards and found the dormer roof OSB wet to the touch! The top of the ridge beam is also wet to the touch.
I know it will be (relatively) easy enough to vent at the far end of the dormer roof - using soffit or fascia vents. However I know I need the air to circulate i.e. vented at both the 'far' dormer soffit end, as well as the ridge end. Am toying with the idea of mushroom vents on top of the dormer roof, but there are 13 openings and obviously I don't want 13 mushroom vents on my dormer roof! (would need one for each opening as there's currently no way for the air to circulate between them)
I'm also thinking I could notch and drill holes in each and every joist to the maximum regulations permitted, that would create some sort of airflow in between joists, and possibly result in needing far less mushroom vents? (could I get away with just 3 - one in the middle and one at each end?) I've attached a diagram showing joist holes and notches I've calculated. I'd have to batten 44mm x 44mm timber to the bottoms of the joists and bring the 120mm Celotex down to that level to allow for 30mm holes to still have the required 50mm height clearance from the hole to the top of the joist.
Also concerned about the roof leaking if I get a roofer to put mushroom vents into a felt roof, whether it's 1, 3 or 14...
Any other solutions to provide ventilation?