Spraggo 1 and 2 ok but all lockshelds fully open?.How do you suggest balancing the system if not with l/s valves?
The trvs will automatically balance the system providing that they are not set to full on. Won`t they???.
Spraggo 1 and 2 ok but all lockshelds fully open?.How do you suggest balancing the system if not with l/s valves?
The trvs will automatically balance the system providing that they are not set to full on. Won`t they???.
Me thinks somene has cut corners and made some dollar! T****r.
Hi spraggo the idea of balancing to to have all the rads heating up evenly, ie the furthest rad the same temp as the nearest rad to the boiler, if you use trvs to try and balance a system the house will heat up very unevenly.
thought you said you would only fit 300L tanks no matter what the needs of the house were 85 t0 210 L is a weight increase of 125 kg lets hope the op floor is strong enoughI would always fit a cylinder large enough to supply the short term demand without relying on reheating.
For a four bed a 210 li is the minimum recommended size!
Tony
My understanding as a novice is that hot water vessels over 15 litres must be kept above 60 for at least an hour a week to prevent the growth of legionella bacteria. Unfortunately, most condensing boilers are most efficient if the return temperature is lower.Ok the tank stat is at 50, turned it down today as Mrs was moaning about how hot the water is coming out of the taps.
ajrobb";p="1800165 said:hobbles";p="1799375 said:Two things that might help:
1. 'Balance' the radiators by adjusting their lockshield valves - this just ensures that the radiator return temperature is typically 11 degrees cooler than the feed with the TRVs wide open. This will help boiler efficiency and generally improve the heat distribution.
What use are TRVs if they are used fully open?.
Adjusting the lockshields is done with the TRVs open to simulate a cold house. Once the radiators are balanced, the TRVs are returned to their normal setting.What use are TRVs if they are used fully open?.
Adjusting the lockshields is done with the TRVs open to simulate a cold house. Once the radiators are balanced, the TRVs are returned to their normal setting.
As long as you appreciate that the boiler can run with a higher return temperature while the house is heating up. This can use up to 10-15% more gas. Once the house is warm, I agree, the TRVs control the flow and there are no efficiencies to be gained (until the room stat starts switching).Thats your choice, no offence but i`ll stick to mine.