514.10.1 of both the BRB and BGB (BS7671:2008 and BS7671:2008(2011) respectively) say that a warning label should be used when an enclosure contains a nominal voltage greater than 230V "where such a voltage would not normally be expected". Those emboldened words clearly are open to interpretation, and maybe were not present in earlier editions.
The "where not normally expected" requirement dates back to the 14th edition:
A.17 Every item of electrical apparatus, or enclosure, within which medium voltage exists and where the presence of medium voltage would not normally be expected, shall be so arranged that before access is gained to live parts, a warning of the maximum voltage present is clearly visible.
As I've just noted with the older definitions elsewhere, medium voltage at that time was defined as being between 250 and 650V. As you say, "not normally expected" is somewhat open to interpretation: Normally expected by whom? You or I might look at the main switchgear for the supply to a larger house and by the nature of that equipment recognize the supply type and thus expect to find 415 or 480V inside. The average householder, not being aware of such things, might "expect" it to be only 240V since that's what he knows he gets from his socket outlets.
The equivalent provision in the 13th edition did not contain the "not normally expected" clause, and required the warning notice in all cases, with a fairly extensive note added to emphasize the point:
109For compliance with Regulation 11 of Part I, terminals and other fixed live parts on which a voltage exceeding low voltage (250 volts) between conductors or to earth may be present shall conform with the requirements of of one of the following clauses (A) or (B), subject to the exemption given below:
(A) They shall be installed in a locked room accessible only to authorized personnel; or
(B) They shall be so enclosed in earthed metal or incombustible insulating material that ready access cannot be had. Unless the points between which a voltage exceeding 250 volts may be present are 6 feet or more apart, means of access shall be marked to indicate the voltage present.
Exemption.- Cables and bare conductors installed in accordance with the requirements of Section 2.
NOTE.- The above requirements apply equally to three-phase circuits in which the voltage between lines or to earth exceeds 250 volts and to groups of two or more single-phase circuits, between which medium voltage may be present, derived therefrom. They apply also to 3-wire d.c. or 3-wire single-phase a.c. circuits in which the voltage between lines or to earth exceeds 250 volts and to groups of 2-wire circuits, between which medium voltage may be present, derived therefrom.
And while on the 13th edition, the requirement about sockets being on the same phase or pole in one room at that time gave a specific floor area of 500 sq. ft. or greater for the exemption to apply.
There are also two differences in 514.10.1 between BRB and BGB:
- 1...In the BGB, "230 volts" has been changed to "230 volts to earth"
I don't have a copy of either the original 17th edition or the new amendment. What's the context in which that appears?
2...To my surprise, the second and third paragraphs of 514.10.1 have disappeared in the BGB. This means that there is no longer a need for warning signs when 'nearby' (can be simultaneously reached) separate enclosures contain voltages >230v relate to one another
Now you quote that, I think it was mentioned on the IET forum a few weeks ago. So that's another relaxation of a long-standing requirement. I wonder if that was done as another part of the "harmonization" process with European standards, since it's long been the norm to have 3-phase supplies in domestic properties in many Continental countries, and seemingly without any of the specific requirements we've had regarding warnings and separation of phases between sockets.
I think the "only one phase for sockets in one room" rule has already gone from BS7671, hasn't it?