Away now until next week, from memory they're all General Electric, box included
How often do you expect the microwave to go wrong?It's a built in microwave though
In that case, the circuit is already at its limit. A new circuit would be best.
Well - not exactly - there is plenty of room.As promised. There's no room for another B20 on the top rail unless the busbar was extended.
One 32A socket circuit (plus a seperate cooker circuit if the cooker is electric) has worked just fine for UK kitchens for donkeys years.North Americans are often accused of having too many separate circuits. However, those in the UK seem to have too few separate/independent circuits.
Thanks for the good sketch and pic.Hello Everyone,
I just want to make sure I'm ok adding this new socket for a microwave.
I plan on putting in a single socket on a 13A fused switch and linking it as a spur from the existing radial circuit. It will be in 2.5mm2 T+E, running from a circuit which is protected by a 20A circuit breaker. The cable will be run in surface trunking over tiles vertically and across in to a cabinet, all sealed safely. On the board, it shares a 63A RCD with four other 20A fuses.
I have attached a diagram showing what is already on it.