That really is not a very helpful statement. Just one double socket is theoretically enough to 'overload' a 13A fuse. As for "diversity calcs", they are essentially impossible for a sockets circuit, unless the designer has a crystal ball.
The whole point of allowing fused spurs (with an 'unlimited' number of sockets) is that the 2.5mm², or maybe 1.5mm², cable will then be adequately protected. Those who cannot think beyond what examples are shown in Appendices to the regs don't seem to understand that, from the point-of-view of cable protection, there's nothing wrong with an unfused spur (from a ring final) supplying multiple sockets if it's wired with 4mm² cable.
Kind Regards, John