It is one that has puzzled me for a while, the Iz for a 2.5mm twin and earth clipped direct (It=27A) when derated for a BS3036 is less than 20A.
 
Sponsored Links



433.1.3 is a qualifier to the basic 433.1.1, which states the overall requirements for how to ensure the correct co-ordination between conductor overload and protective device.



i.e. you start with 433.1.1 defining the Ib <= In <= Iz and I2 <= 1.45Iz relationships.

433.1.2 says that where the protective device is a <list of types> if you do Ib <= In <= Iz you'll automatically have done I2 <= 1.45Iz.

433.1.3 says that if you have a BS3036 you need to go for In <= 0.725Iz in order to achieve I2 <= 1.45Iz, i.e. it's the special consideration for that design which you need to make to ensure compliance with 433.1.1.

433.1.4 has the special consideration you need to make for 20° buried cables to ensure compliance with 433.1.1.

And our old chum 433.1.5 has the special considerations for ring finals, including those using 30A BS3036s, which you need to make to ensure compliance with 433.1.1.

Like I've always said, it's a kludge designed to regularise an established practice, which was brought into being for reasons of expediency, and would not otherwise comply. If radials were all we had ever had, and 433.1.1 - 433.1.4 were the only regs we had ever had which prescribed the correct co-ordination between conductor overload and protective device, do we really think that a wiring committee would say "tell you what, let's allow undersized ring finals and write a special regulation which basically says ignore the previous 4 regulations and do this because it will be OK"?

They should be consigned to history. Simply remove 433.1.5, then as circuits get modified the protective devices have to be replaced with 20 or 25A ones. Would make the whole issue of spurs much easier too.

And there would always be the option to find a logical place to split the ring and turn it into two radials. (You could even leave the cpc as a ring, as per 543.7.2.1(ii)(c), if you want to retain the resilience it offers.)
 
And there would always be the option to find a logical place to split the ring and turn it into two radials. (You could even leave the cpc as a ring, as per 543.7.2.1(ii)(c), if you want to retain the resilience it offers.)

don't start that again BAS...... ;) :eek:
 
Sponsored Links
But what if you then put that cpc on a plane on a conveyor: would it take off?
 
Only if as it got thinner the voltage decreased and the current increased to compensate, and if you touched your titanium bodied camera to the neutral.
 
A great mass debate!

Surely the point is that regs require all circuits to be 'designed' but in order to save us all reinventing the wheel each time the IET have set out 3 standard circuits for us to reuse.
Their statement is if you stick to the requirements of these designs no futher calculations are required. so taking a spur from ring at source is ok
Type A1.
However for a radial type A2 on 2.5 it must be fused at 20A or less.
4 pages of discussion over what is laid down in simple terms with drawings in appendix 15......come on fellas!
 
However for a radial type A2 on 2.5 it must be fused at 20A or less.
4 pages of discussion over what is laid down in simple terms with drawings in appendix 15......come on fellas!

So whilst carrying out a PIR you come across an installation where a 30/32A OPD supplies a socket or FCU, do you:

a) Say that can't be - that circuit arrangement isn't listed in apprendix 15 (informative) :eek:
b) Look further into BS7671:2008 (normative) to see if it's a valid circuit arrangement

Depending on you answer, would you note the arrangement as an observation? What code and recommendation would you give?

Anyway, it's discussions like this that make this forum interesting.
 
433.2.2 specifically says

433.2.2 The device protecting a conductor against overload may be installed along the run of that conductor in the part of the run between the point where a change occurs ( in cross-sectional area, method of installation, type of cable or conductor, or in environmental conditions ) and the position of the protective device has neither branch circuits nor outlets for connection of current-using equipment and fulfills at least one of the following conditions:

(i) It is protected against fault current in accordance with the requirements stated in Section 434
(ii) It's length does not exceed 3 m, it is installed in such a manner as to reduce the risk of fault to a minimum, and it is installed in such a manner as to reduce to a minimum the risk of fire or danger to persons ( see also Regulation 434.2.1 )

please note the highlighted section..
would you consider a single or double socket an "outlet for connection of current-using equipment"?

your follow on argument will likely be that the plugs all contain fuses...
but it doesn't specify that and that's not entirely true either..
there are special "red" plugs that contain no fuse.. while these are not in general use they are fitted to some protable machines that have large current demands for a short duration, such as portable x-ray machines..

while the example of the hand dryers would satisfy 433.2.2 in some way if the faut current requirements were met, this is only because they have permanent connections and not outlets...

I would read the regulations as
outlets for connection of current-using equipment
to mean as a branch not at end of line.

However I have quoted what you have written because of the 3 meters rule. Very basic I know but spurs have a maximum of 3 meters so to original question.

can you have just a single or double socket wired in 2.5mm² from a 32A breaker?

Yes but maximum of 3 meters in length.

The cable type and routing is of course important and with Ali-tube cable being designed for partition walls even if not as yet widely used one must consider the use of cable rated to 90 degrees even if you don't want to include mineral insulated cable.

Since 2.5mm cable (90 deg) is rated at 33A clipped direct the fact that the regulations say we can use 2.5mm on a spur does not mean it says anywhere we can over load cable as we could be using Ali-tube clipped direct and we as the electrician must therefore decide when we fit cable below the rating for the automatic disconnection device if we are doing something dangerous.

Back to
(ii) It's length does not exceed 3 m, it is installed in such a manner as to reduce the risk of fault to a minimum, and it is installed in such a manner as to reduce to a minimum the risk of fire or danger to persons ( see also Regulation 434.2.1 )
and I am afraid many electricians don't consider that they just do it that way because they have always done it that way.

The BS7671:2008 was not written by one man. And I am sure we all agree it still has errors (RCD on SELV for example) and as a result I can't understand why people have such faith in inspectors from their club. They can miss read a regulation just the same as us.

134.1.1 says we should follow manufactures recommendations who have produced a cable specially for our new walls so if we don't use Ali-tube are we in breach of regulations? Especially now "Rule of thumb" has become history! No I am sure we can continue to use twin and earth but I do think some thought should be given to the run and it should no longer be. I've always done it that way so why change now!
 
OK you can comply with 434 instead but that says:-
434.2.1 The regulations in Regulation 434.2 shall not be applied to installations situated in locations presenting a fire risk or risk of explosion and or where the requirements for special installations and locations specify different conditions. Amended July 2008

Except where Regulation 434.2.2 or 434.3 applies, a device for protection against fault current may be installed other than as specified in Regulation 434.2. under the following conditions:

The part of the conductor between the point of reduction of cross-sectional area or other change and the position of
the protective device shall:
(i) not exceed 3 m in length, and
(ii) be installed in such a manner as to reduce the risk of fault to a minimum, and
NOTE: This condition may be obtained. for example, by reinforcing the protection of the wiring against external influences
(iii) be installed in such a manner as to reduce to a minimum the risk of fire or danger to persons.

Oh dear back to 3 meter rule I see!!!!!

Yes there are some special places where it is allowed to use no protection but this hardly applies to a house.
 
that's only ONE section of 434 and the one that deals with the placement for the device for fault protection at that....


and your reading of the other reg is also flawed..



has neither branch circuits nor outlets for connection of current-using equipment

the important word there is NOR...
this means that the outlets don't HAVE to be on the branches....
 
Oh dear back to 3 meter rule I see!!!!!

Yes there are some special places where it is allowed to use no protection but this hardly applies to a house.

Eric, are you saying that a spur from a ring final including when originating from the consumer unit should be less than 3 meters?

I'm not sure I agree with you.
 
Oh dear back to 3 meter rule I see!!!!!
But not at all for double sockets, as there is a branch before the protective device (fuse plug).

I was thinking it would all be covered by 433.3.1 (ii) but having read it again I think it could not apply to socket outlets as overload current is still possible.

So to answer the original question

ColJack said:
can you have just a single or double socket wired in 2.5mm² from a 32A breaker?
... I would like to change my answer from a blanket yes to yes up to 3m (single), and no (double).
 
... I would like to change my answer from a blanket yes to yes up to 3m (single), and no (double).

mfarrow, are you saying that a spur from a ring final including when originating from the consumer unit should be less than 3 meters?

If not then what's the difference?
 