Thanks namsag, apparently although in the brochures they are not yet available for another six months.
You need to get a Honeywell Chronotherm stat, this is wireless and will modulate your boiler, see the following link
http://europe.hbc.honeywell.com/products/ecatdata/pg_cm920.html[/QUOTE]
The CM900 series of programmable thermostats are not modulating controllers; they are PI (proportional-integral) controllers which mimic the effect of a true modulating controller.
All they do is adjust the proportion of time that the boiler is on. When the room temperature is low the boiler runs continuously until the temperature is within 1.5°C of the set temperature. It then goes into an on-off cycle based on a 10 minute period, e.g 9 minutes on, 1 minute off. The ratio changes as the temperature approaches the set temperature.
A true modulating controller acts directly on the burner so the boiler output is reduced as the set temperature is reached.
the honeywell cm 927 is not a modulating stat
there is a honeywell cm 957 that is wireless and modulating, check their
website for details
EDIT after confirmation from mehran
As far as I understand it, the aim of the CM900 and the earlier CM67 series was to reduce the over- and under-shoot typical of most thermostats which keep the boiler running at full output until the thermostat reaches the set temperature. The boiler will cut out but, due to the heat in the radiators, the room wil continue warming up, maybe a degree or more. Users will feel too warm, so they turn the thermostat down. But then the temperature drops too low before the boiler comes on again; so they turn the stat up. A vicious cycle of turn up/turn down.... one of the aims is to stop the boilers cycling on and off, this flys in the face of that philosophy.
Cheers
And you had Vaillant weather compensation, which had to be removed because it would not cope with your single rad upstairs zone! Do you live in a bungalow by any chance?I agree with you D_Hailsham, our Vaillant 937 is set at 16kw and the flow temperature could be set at 75C for example, the boiler will fire at the full 16kw and modulate down as it approaches 75C. You'd have to adjust the kw regularly in d.0 if you wanted the boiler to fire according to how cold it is outside......that's how I see it and many of you know better
Well I spoke to Honeywell and the open therm stats are not avaiable untill September so I guess we need to watch this space.
My understanding of the "open them" principle is that the device (either a room stat or weather compenstor) simple tells the boiler what the actaul temp is and the boiler works out the rest based on a programmed curve, this curve can be modified by adjusting other parameters within the boiler.
Again I hope i've got this right any more info would be appreciated.
My understanding of the "open them" principle is that the device (either a room stat or weather compenstor) simple tells the boiler what the actaul temp is and the boiler works out the rest based on a programmed curve, this curve can be modified by adjusting other parameters within the boiler.
Again I hope i've got this right any more info would be appreciated.