There's nothing wrong with a 'star' radial, and no need to protect it with a 16A OPD unless the (2.5mm²) cable is deeply embedded in insulation (Method 101).Yes I know there are lots of 20a radials. The one I'm refering to was wired as a spider with 1 central junction box so I felt that it wasn't the best to be installing it at 20amps so limited it to 16a
Kind Regards, John